Hello Fabian,
Thanks for your reply,
For information I can't change the CNT because, after this point I take a picture from a camera that is attached to the robot flange. However I will try to slow it down and I will let you know.
Hello Fabian,
Thanks for your reply,
For information I can't change the CNT because, after this point I take a picture from a camera that is attached to the robot flange. However I will try to slow it down and I will let you know.
Ok, so I tried slowing it down and even increase the CNT (for testing) but it didn't change, I have the same message 'Over payload change distance' and the same stop.
Looking at the error
Error | Severity | Message | Cause | Remedy |
R30BP:SYST-324 | Payload number is changed | When the payload change distance of Collaborative Robot is disabled, the payload number has been changed. | You can avoid to pause a program to change the payload number when the payload change distance is enabled. |
I don't have a cobot, but the payload variables on a regular robot are $PLST. Maybe you can find the variable to disable it
Hi Fabian thanks for your information,
I do have $PLST variables (see the atachment) but I didn't find anything like 'Payload change distance'.
Bu as you can see (I hope), I have a variable named $PLST_OVLD that I thought was probably the meaning of my problem, but when I try to set it to true I have a message 'Variable/field write-protected'.
Do the variable $PLST_OVLD mean something to anyone? Or if it's not related at all ?
Hi Theo,
I have just joined the forum and wanting to do something similar. May I ask what kind of barcode scanner did you use and how is it connect to the HMI?
Thank you.
Hello Frank Yeh,
Welcome !
I use a SYMBOL LI2208 barcode scanner, you can find it on amazon (https://www.amazon.com/Symbol-LI2208-…t/dp/B00EUN0M8I). And it's connected to my HMI by USB.
Theo.g thank you for the information sir. Is the scanner being called upon by a Karel program and processed to change register values?
.. I don't have a PLC, The HMI I'm using is a Proface SP5000 series communicating with the robot in ethernet/IP and using SNPX..
.. And it's connected to my HMI by USB.
hermann thank you sir! I am not as familiar with the HMI side of things. I will look into it.