KRC1 Device Net configuration
  • legityme
  • April 16, 2021 at 1:39 PM
  • MOM
    176
    7
    1,424
    • May 20, 2021 at 9:42 PM
    • #41
    The content of the devnet.ini is more or less the same.
    The big difference is the driver
    - dndrv.o for Kuka System Software running under Win95
    - dn2drv.o for Kuka System Software running under WinXPe (like KSS V5.6.9)
    normally base system driver for Win95 systems most of the time are not compatible with base system driver for WinXPe systems (even if they have the same name)
    If the complete CD is missing you could give KUKA the serial number of your robot and ask for a copy of the cd or at least for the dndrv.o for your system.
  • legityme
    85
    • May 25, 2021 at 1:43 PM
    • #42
    Hello guys!
    I think everything is working now. I managed to get the dndrv.o driver for KRC1 from KUKA and managed to put on the drivers folder. As soon as I turned the controller on, all the errors related to the device net configuration were gone. I tried to set an output to true and now the LEDs on the KL2809 does light. The jumps I made to test out the KL1809 (input card) worked too.
    Thank you all very much for the support!
  • markopo
    207
    • May 26, 2021 at 10:37 AM
    • #43
    I have this error during config devicenet.
    What could be wrong ?
    Images
      • 367.62 kB
      • 1,600 × 1,200
      • 43
  • panic mode
    1,300
    13,143
    • May 26, 2021 at 2:19 PM
    • #44
    you may want to change GUI language to English before taking screenshot... and resize the columns so message number is visible or show them individually.
  • markopo
    207
    • May 26, 2021 at 2:37 PM
    • #45
    Hi panic mode.
    Im using Allan Bradley module with i/o's.
    Ive got this errors in devnet.log
    Images
      • 210.7 kB
      • 1,600 × 1,200
      • 24
  • markopo
    207
    • May 26, 2021 at 2:38 PM
    • #46
    devnet.log 1
    Images
      • 166.71 kB
      • 900 × 1,200
      • 35
  • markopo
    207
    • May 26, 2021 at 2:39 PM
    • #47
    devnet.log 2
    Images
      • 207.59 kB
      • 900 × 1,200
      • 19
  • markopo
    207
    • May 26, 2021 at 2:40 PM
    • #48
    devnet.ini
    Images
      • 137.14 kB
      • 900 × 1,200
      • 27
  • markopo
    207
    • #49
    iosys.ini
    Images
      • 410.52 kB
      • 1,600 × 1,200
      • 37
  • panic mode
    1,300
    13,143
    • May 26, 2021 at 2:53 PM
    • #50
    well, part that was not mentioned before is that you are using AB Point IO.
    I have used PointIO with EIP, not the DeviceNet but as i remember they are not straight forward as most of the other products because they always needed to be configured. In case of 1734-AENT this was possible through web browser...
    ... and in case of DeviceNet version (1734-ADN) there is no Ethernet port, so you need to have RSNetWorx for DeviceNet to configure it or ... you will be stuck.
    https://literature.rockwellautomation.com/idc/groups/lit…um002_-en-p.pdf
  • markopo
    207
    • May 26, 2021 at 3:47 PM
    • #51
    panic mode precious information for me as always
    I don't even know how to do it
    I will swap Io device for other vendor which is straight to connect, in meantime I will make huge step to be familiar with AB point IO.
  • SkyeFire
    1,061
    9,465
    • #52
    Yes, I just went through this with that exact same AB module.
    Bottom line: the I/O "slices" are all factory-configured for the same address on the 1734's backplane. That entire module (1734 plus the I/O slices) must be set up using RSLogix before it can be connected to a robot.
    It also turns out that the default I/O modes are tricky -- you have to deliberately set them all to Polled. Strobe, Change Of State, and Cyclic are other options, but Polled is the only one I'm sure will work with a KRC's DN driver.
    Also, I don't try reading code or errors off of photos. My eyes just aren't up to it anymore. Transcribe or copy&paste actual messages and log contents.
  • markopo
    207
    • May 27, 2021 at 9:58 AM
    • #53
    Skye thanks for reply.
    Main errors in log are for interrupt and no ability to run instance. I've checked configuration devicenet on vss 5.4.7 hf4 and kss 5.4.11 same errors. I was wondering it could be problem with kss which originally doesn't work with mfc 3.02 but i run vss which works smoothly with mfc 3.02.
    Now as You said I'm stuck with AB point IO.
    Looking for Wago , Wago needs some special configuration or is straight ?
  • SkyeFire
    1,061
    9,465
    • May 27, 2021 at 7:14 PM
    • #54
    It's been a few years since I used Wago, but I recall it being fairly straightforward -- all polled, and as you add slices, the bus coupler increases the "size" of bytes in/out, which you can see using the 'dnwho' commands via Telnet. Wagos only got a bit odd if you started mixing analog and digital -- the ordering of the bytes on the bus was based on the I/O type, rather than the physical order of the slices.
  • markopo
    207
    • May 28, 2021 at 9:28 AM
    • #55
    SkyeFire nice to hear You.
    The main problem is when I'm using command in run Telnetk 192.0.1.1 using dnWho command was not recognized :frowning_face:
  • markopo
    207
    • May 28, 2021 at 9:47 AM
    • #56
    Functions in telnet must be used with exec for example: exec "dnWho"
  • SkyeFire
    1,061
    9,465
    • May 28, 2021 at 3:37 PM
    • #57
    The telnet commands changed a few times over different versions of KSS. Since this is a KRC1, it probably used the older type of the command, that did not use the "exec" prefix.
    Files
    DevNet Telnet Notes.txt 2.62 kB – 23 Downloads KUKA Telnet.txt 2.05 kB – 25 Downloads DevicenetErrors.txt 1.82 kB – 21 Downloads
  • markopo
    207
    • June 15, 2021 at 4:46 PM
    • #58
    SkyeFire thanks for answer.
    I was using docs where was
    Pin 1 - 0V
    Pin 5 -24V
    I've swapped power supply and can_hi and can_low and it works.
    Images
      • 259.31 kB
      • 1,600 × 1,200
      • 11
  • panic mode
    1,300
    13,143
    • June 15, 2021 at 5:03 PM
    • #59
    this agrees with my experience. in most cases (by far) problem is the faulty wiring, not configuration...
  • krc1
  • DeviceNET