AAD04A Analog Input Card Refresh Rate
  • KyleW
  • February 2, 2021 at 2:35 PM
  • KyleW
    7
    41
    I am having an interesting issue where the analog input is updating extremely slowly. I have a laser sensor that outputs 0-10V, this signal wire is landed on V+, the V- has the same ground that the sensor is using and com and v- are connected.
    I can see on the multimeter the sensor output switch from 0 -> 10V instantly but on the card it's updating at about 35/sec (0-600, respective to my 0-10V).
    Anyone have any idea why my refresh rate would be so slow?
    It's on a R30iB controller.
  • HawkME
    568
    3,268
    • February 2, 2021 at 5:28 PM
    You said 35/sec ... So 35 updates per sec or 1 update every 35 seconds?
    35 updates per second is about 28 milliseconds so that doesn't seem too bad.
  • Nation
    Typical Robot Error
    542
    1,924
    • February 2, 2021 at 5:58 PM
    According to the specs, the input filter delay on that card is 50ms, or 20Hz. Sounds like you are doing a bit better than that.
    If you need speed, you will have to buy an AAD04B2 module. It runs at 500Hz.
  • KyleW
    7
    41
    • February 2, 2021 at 6:45 PM
    What I mean by 35/sec is I can watch the analog input slowly climb till it maxes out. If I switch the input from 0V to 10V instantly, the input goes from 0-600, but not instantly, it takes about 20seconds. And similarly when switching from 10V to 0V.
    I thought that it takes in whatever voltage it's getting and converts that to an output, and would do this conversion at 20HZ?
  • HawkME
    568
    3,268
    • February 2, 2021 at 7:19 PM
    Ok so you mean 35 seconds not 35/sec. That doesn't seem right.
  • Nation
    Typical Robot Error
    542
    1,924
    • February 2, 2021 at 7:27 PM
    Sounds like a wiring issue if it it preforming like that. Are the grounds of the robot and the analog signal source linked together?
  • KyleW
    7
    41
    • February 2, 2021 at 7:48 PM
    HawkME, I mean the analog value is changing at 35/sec. When I switch the voltage from 0->10 the analog value after 1 second is around 35, not at 600 like it is after I let it settle for ~20sec.
    Nation, I just checked and they are the same.
  • SkyeFire
    1,052
    9,429
    • February 3, 2021 at 2:41 PM
    That sounds a lot like a large capacitance on the line somewhere. I would suggest putting a high-impedance meter directly on the input contacts of the analog card (not at a distance along the input line), and monitor the voltage change there. Or plug a reference test voltage directly into the analog input card with a short, clean pair of wires.
    If the analog card response is still laggard even with the input line eliminated, the card may be suspect.