What is the plant voltage you are supplying to the DX100 controller? Did you check the connections on the transformer in the two DX100 controllers to make sure they are set to the correct incoming voltage. If this is all correct, you are probably dropping one phase of your supply causing the other two phases to go high and blow the fuse.