Kuka KRC2 Devicenet repeating Inputs and Outputs over different addresses?
  • Hello, i have a issue with the configuration of the DeviceNet (MFC card). i have remote I/O units (Festo Values Ch5 2x8 Input and 9 outputs) and a (unit Ch 6 2x8 input and 2x8 Output)
    But problem is that when i have inputs from the unit ch5 DI0 i see in the KRC Input $IN[17] and $IN[33] and so on.
    so it is somehow repeating the inputs.?
    the adresses $IN[33] should be connected to the Other unit Ch6 DI0 but that one is not working at all. it all works when i only connect one unit. but when i have both it is not working. hope i just do something stupid.
    I have configured devnet.ini as:
    [krc]
    debug=1
    baudrate=125
    LOGFILE=1
    [1]
    macid=5
    [2]
    macid=6
    IOSYS.INI as:
    ; IOSYS.INI - Configuration file for the IO-System
    ; For configuration help go to the end of this file.
    [CONFIG]
    VERSION=2.00
    [DRIVERS]
    MFC=0,mfcEntry,mfcdrv.o
    DEVNET=2,dnInit,dndrv.o
    [MFC]
    INW0=0 ;$IN[1-16]
    OUTW0=0 ;$OUT[1-16]
    OUTW2=2 ;$OUT[17-32]
    [DEVNET]
    INB2=5,0,x1 ;$IN[17-24]
    INB3=5,1,x1 ;$IN[25-32]
    INB4=6,0,x1 ;$IN[33-40]
    INB5=6,1,x1 ;$IN[41-48]
    OUTB4=5,0,X1 ;$OUT[33-40]
    OUTB5=6,0,x1 ;$OUT[41-48]
    OUTB6=6,1,x1 ;$OUT[49-56]
    [END SECTION]
    kind regards, Marc
  • it's been long time since i dealt with KRC1/KRC2 and even then i always mapped I/O using smallest unit (byte).
    can you check of this is the issue:
    OUTW0=0 ;$OUT[1-16]
    ; OUTW1=1 ;$OUT[17-32]
    OUTW2=2 ;$OUT[33-48]
  • That will fix the problem, but the reason is:
    You have installed the older Devicenet driver dndrv.o. (in comparison to dn2drv) :)
    With that driver the entrys in iosys.ini have a different Form than you used.
    All inputs and outputs are counted over all units, there is no number of the unit in the definition line. I. E. :
    [DEVNET]
    INB2=0 ;$IN[17-24]
    INB3=1 ;$IN[25-32]
    INB4=2 ;$IN[33-40]
    INB5=3 ;$IN[41-48]
    ; the same for output...
  • Oke Hermann,
    so i have 2 units channel 5 and 6 is this than the correct way ?
    [DEVNET]
    INB2=5 ;$IN[17-24]
    INB3=5 ;$IN[25-32]
    INB4=6 ;$IN[33-40]
    INB5=6 ;$IN[41-48]