I see a few things that are wrong.
Signal timing is off. It shows all three signals coming on at the same time PNS bits, PNS Strobe and Prod start. This is wrong. It should be as follow.
1. PNS select bits come on
2. wait 100 ms
3. PNS strobe turns on
4. wait 100 ms
5. Prod Start signal comes on
6. wait 100 ms
7. PNS Strobe and Prod start go off
Please fix the timing sequence to ensure a reliable startup.
Second you do have another error. Startup Check failed. Which should be accompanied by another message in the alarm history showing which check failed. You can view the startup checks on the Prog Select screen. Please take a screen shot of that and post which startup checks are enabled. Then you can go through each one that is enabled and see which one is causing the error.