KR200C tripping out rccd

  • Yorrite
  • July 17, 2020 at 9:45 PM
  • Thread is Unresolved
  • Yorrite
    Trophies
    4
    Posts
    26
    • July 17, 2020 at 9:45 PM
    • #1

    I have a KR200C which has been super reliable for years, but now my landlord has upgraded the building's electrical system and included an RCCD.

    The robot boots up fine but as soon as I go to jog it, or start a program the RCCD trips. We've tried both a 100ma and a 300ma RCCD and both trip out.

    I'm not sure what is the likely culprit (Power supply?) or if there's a known likely problem with these Kukas.

    Power is from a regular 3 phase supply and the electrician checked that the phase rotation is correct.

    Any ideas please...

  • Event Robotics
    Reactions Received
    7
    Trophies
    3
    Posts
    62
    • July 18, 2020 at 9:46 AM
    • #2

    Hi,
    There is nothing wrong with the robot.
    We use our robots in different locations a lot, and have these problems sometimes.
    300ma should be ok normaly, but it can be different between brands.
    Ask the electrician if he can try a different brand or a higher amp rate.

  • Elia_
    Reactions Received
    5
    Trophies
    3
    Posts
    18
    • July 18, 2020 at 11:59 AM
    • #3

    Phase order doesn't matter for a robot, the mains input feeds a 3-phase rectifier, everything beyond that is powered off a DC bus (note: some KRCs have 3-phase cooling fans, where it *might* make a difference, but not necessarily, depending on the fan geometry). The problem is that servo drives and servos on a robot this size are a ginormous energy sink when they start. It doesn't help that there's no galvanic separation from the mains all the way up to the motors, so any actual leakage that does happen counts against the RCD limit.

    Is KR200C modern enough to have six separate servo drives and independent brakes? Try jogging A6 only, maybe try disconnecting A4 and A5 motors for that test, too (robot shouldn't notice as long as you don't try to move them, they won't be affected by gravity even with brakes open). I'm not sure if the result is going to be of any practical significance even if it doesn't trip the RCD, maybe it could help you convince the electrician to provide a circuit with no RCD ("See? Nothing wrong with it, just pulls too much power in an instant when all six motors start together.")

  • Yorrite
    Trophies
    4
    Posts
    26
    • July 18, 2020 at 12:28 PM
    • #4

    Thanks for the replies, I'd an idea it might be a regular problem.

    Getting a power feed without an RCCD would be favorite, but would be meet with a lot of resistance (and cost?) from my landlord.

    300ma seems to be the maximum RCCD rating but I've now discovered that it's possible to get a 300ma RCCD with a time delay so that's the next thing to try...

  • javaman
    Reactions Received
    5
    Trophies
    4
    Posts
    309
    • July 18, 2020 at 2:13 PM
    • #5

    i have also a 30mA type AC RCD and trips sometimes when i try to jog and every time

    i shutdown the krc2 controller.

    I have contacted kuka and told me that krc2 needs 300mA RCD

    type F is the correct type that is needed but because it costs more than 500 euros

    you can try a 300mA type A RCD that is cheap (< 50euros).

    If 300mA trips there is more that 300mA leakage..

    rest electric installation is correct ? neutral and PE must be connected together before RCD...

    Only 30mA RCD protects humans

    300mA RCD protects from leakage only the machine NOT humans 300mA for humans are deadly.

    Edited once, last by javaman (July 18, 2020 at 2:26 PM).

  • Event Robotics
    Reactions Received
    7
    Trophies
    3
    Posts
    62
    • July 18, 2020 at 2:18 PM
    • #6

    In what country are based ?
    It depends on local regulations if you need an RCD in a industrial situation.

  • javaman
    Reactions Received
    5
    Trophies
    4
    Posts
    309
    • July 19, 2020 at 11:53 AM
    • #7

    Read this https://www.electrical-installation.org/enwiki/Types_of_RCDs

    B is the correct type of RCD to install but the problem is that cost about 600 euros.

    Type A costs under 50 euros.

    Leakage is from line filters in krc2 cabinet.

  • Yorrite
    Trophies
    4
    Posts
    26
    • July 19, 2020 at 12:25 PM
    • #8

    Thanks Javaman that article is really informative.

    Checked out type B and it's £400 plus tax so not keen! Has to be 100amp because it's at the mains feed for the whole site.

    We are going to try a time delay 300mA breaker this coming week which I think will cost about £225 this coming week.

    Not sure of the regs here in the UK but I'm sure the electrician will know...

  • javaman
    Reactions Received
    5
    Trophies
    4
    Posts
    309
    • July 20, 2020 at 12:46 AM
    • #9

    NO each robot needs it's own RCD not one central RCD for all installation..

    For example a cheap option is 40A/300mA/type A RCD under 50 euros and should work.

  • Yorrite
    Trophies
    4
    Posts
    26
    • July 21, 2020 at 9:25 PM
    • #10

    We fitted a 300mA delay RCD today and tested everything running together (Robot, Rotary table, and Spindle) and all seems good.

    The RCD is a Schneider SED100304S which is rated at 100A with 4 poles and a delayed trip, it serves the whole site.

    Bit early to say for sure that the problem is solved but fingers crossed...

  • javaman
    Reactions Received
    5
    Trophies
    4
    Posts
    309
    • July 21, 2020 at 10:58 PM
    • #11

    Not solved 100% because 300mA are deadly for humans.

    This is leakage protection only for machine not for humans.

    Perhaps the best solution is 30mA type B but i don't know if it works 100% and it costs about 500-600euros

    Next best solution is type A 300mA with very good ground

  • Wall-E
    Reactions Received
    3
    Trophies
    3
    Posts
    245
    • December 15, 2021 at 7:40 PM
    • #12

    Hi folks !

    The recommended RCD can be found in the integration manual for a specific controller generation / robot.

    It is also dependent on the size of the cabinet.

    In my case it's a 300mA version, with 3x25A and retarded action, type "Ai", "SI" , "HPI" or "F" depending on fabricator.

    What I don't understand in my documentation is that it specifies a three phase RDC with no neutral.

    My electricial put a 4 pole RDC (3 phases + Neutral), and I have no idea if the Neutral is grounded.

    The X1 wiring schematic marks the Neutral as an "Option for service socket".

    I have no idea what that means.

    In short, I'd like to know what to do with the damn Neutral lead...

  • panic mode
    Reactions Received
    1,267
    Trophies
    11
    Posts
    13,033
    • December 17, 2021 at 4:33 AM
    • #13

    it is exactly as described. KRC4 does NOT use neutral.

    but if you want to add an OPTIONAL service receptacle (230VAC single phase outlet) so that service technician can plug his laptop or phone charger or whatever, then you DO want the N wired as well.in most of the world three phase supply is 400VAC phase to phase. but that also means that phase to neutral is 230V.

    if you are in Americas and use NA version of the controller, those units do not use Neutral conductor. This is because they use transformer and 120VAC output is obtained from single phase secondary (500VA max)..

    1) read pinned topic: READ FIRST...

    2) if you have an issue with robot, post question in the correct forum section... do NOT contact me directly

    3) read 1 and 2

  • Wall-E
    Reactions Received
    3
    Trophies
    3
    Posts
    245
    • December 17, 2021 at 2:50 PM
    • #14

    Got It. I'll just unplug the Neutral.

    What worries me is all that fuss about the "neutral having to be grounded".

    If Neutral isn't plugged in X1, what difference would it make if it wasn't grounded ?

    As I mentionned, I experienced first hand that the neutral and the ground are NOT at the same potential in my workshop because I tripped the RCD when cutting a 220V single phase wire.

    I'm sure that the switch was off, so the phase wasn't "hot".

    I even came to wonder if that's why one of my KSPs went bad...

  • hermann
    Reactions Received
    404
    Trophies
    9
    Posts
    2,595
    • December 19, 2021 at 7:13 AM
    • #15
    Quote from Wall-E

    .. I even came to wonder if that's why one of my KSPs went bad..

    No. As you see, neutral isn't used inside the cabinet of the Kuka, so it can't be a problem if you connect it to the x1. The wire ends there

    Quote from Wall-E

    I tripped the RCD when cutting a 220V single phase wire.

    How did you do that exactly? Did you use an unisolated cutter?? Or did you cut a 3 wire cable with one cut?

  • panic mode
    Reactions Received
    1,267
    Trophies
    11
    Posts
    13,033
    • December 19, 2021 at 2:55 PM
    • #16

    Read the spec. Spec is not written for Germany or France only. It is universal and shall be followed everywhere around the world

    Grounded neutral is grounded at the supply... By grounding center of the WYE (secondary of the supply) you are ensuring to meet another KRC spec requirement - all phases are balanced or symmetrical about neutral or ground. Some places have unusual supply with corner grounded delta. This is not compatible with KRC and requires isolation transformer. Your electrician should know know all this.

    1) read pinned topic: READ FIRST...

    2) if you have an issue with robot, post question in the correct forum section... do NOT contact me directly

    3) read 1 and 2

  • Wall-E
    Reactions Received
    3
    Trophies
    3
    Posts
    245
    • December 21, 2021 at 9:47 AM
    • #17
    Quote from hermann

    How did you do that exactly? Did you use an unisolated cutter?? Or did you cut a 3 wire cable with one cut?

    Yes, I'm a morron. I cut the three cables at once. But as I said, the phase was out, so the short came from connecting earth and neutral.

  • Wall-E
    Reactions Received
    3
    Trophies
    3
    Posts
    245
    • December 21, 2021 at 9:55 AM
    • #18
    Quote from panic mode

    Grounded neutral is grounded at the supply... By grounding center of the WYE (secondary of the supply) you are ensuring to meet another KRC spec requirement - all phases are balanced or symmetrical about neutral or ground. Some places have unusual supply with corner grounded delta. This is not compatible with KRC and requires isolation transformer. Your electrician should know know all this.

    The Electrician told me that in France, Earth and Neutral are grounded by the utility.

    It is forbidden to do it in your own installation.

    He told me that sometimes, there car ne a slight potential difference because between the source and the plug, there can be induced currents in the Earth and Neutral ; this is what tripped my RCD when I cut my cables.

    But I have no idea if this is a problem for my Robot. I might be worrying for nothing, but it still isn't a clear-cut case for me.

    As per my electrician, he probably isn't the sharpest tool in the shed. He put a local "D" curve RCD for my dedicated robot line, but left a standard main RCD for the workshop. Now the latter is tripping each time I shut the controller :frowning_face:

  • hermann
    Reactions Received
    404
    Trophies
    9
    Posts
    2,595
    • December 21, 2021 at 9:57 AM
    • #19

    Then the behaviour is normal. When you cut the wire neutral and earth is connected and build a parallel resistor with a very small value, but never the less a small current will go through the earth line because there always exist a very small potential difference between earth and neutral, when other devices are connected on the same fuse (not the RCD).

    Edit: The robot has no problem with the neutral, he doesn't use it. It is not wired inside the cabinet.

    If RCD are cascaded they must be selective, see: https://www.electrical-installation.org/enwiki/Coordin…tective_devices

    In your installation they are selective, but the wrong way :winking_face:

  • Wall-E
    Reactions Received
    3
    Trophies
    3
    Posts
    245
    • December 21, 2021 at 10:57 AM
    • #20
    Quote from hermann

    In your installation they are selective, but the wrong way

    Yep, I guess that sums it up nicely.

    Thanks Hermann !

Advertising from our partners

IRBCAM
Robotics Channel
Robotics Training
Advertise in robotics
Advertise in Robotics
Advertise in Robotics

Job Postings

  • Anyware Robotics is hiring!

    yzhou377 February 23, 2025 at 4:54 AM
  • How to see your Job Posting (search or recruit) here in Robot-Forum.com

    Werner Hampel November 18, 2021 at 3:44 PM
Your browser does not support videos RoboDK Software for simulation and programming

Tag Cloud

  • abb
  • Backup
  • calibration
  • Communication
  • CRX
  • DCS
  • dx100
  • dx200
  • error
  • Ethernet
  • Ethernet IP
  • external axis
  • Fanuc
  • help
  • hmi
  • I/O
  • irc5
  • IRVIsion
  • karel
  • kawasaki
  • KRC2
  • KRC4
  • KRC 4
  • KRL
  • KUKA
  • motoman
  • Offset
  • PLC
  • PROFINET
  • Program
  • Programming
  • RAPID
  • robodk
  • roboguide
  • robot
  • robotstudio
  • RSI
  • safety
  • Siemens
  • simulation
  • SPEED
  • staubli
  • tcp
  • TCP/IP
  • teach pendant
  • vision
  • Welding
  • workvisual
  • yaskawa
  • YRC1000

Thread Tag Cloud

  • abb
  • Backup
  • calibration
  • Communication
  • CRX
  • DCS
  • dx100
  • dx200
  • error
  • Ethernet
  • Ethernet IP
  • external axis
  • Fanuc
  • help
  • hmi
  • I/O
  • irc5
  • IRVIsion
  • karel
  • kawasaki
  • KRC2
  • KRC4
  • KRC 4
  • KRL
  • KUKA
  • motoman
  • Offset
  • PLC
  • PROFINET
  • Program
  • Programming
  • RAPID
  • robodk
  • roboguide
  • robot
  • robotstudio
  • RSI
  • safety
  • Siemens
  • simulation
  • SPEED
  • staubli
  • tcp
  • TCP/IP
  • teach pendant
  • vision
  • Welding
  • workvisual
  • yaskawa
  • YRC1000
  1. Privacy Policy
  2. Legal Notice
Powered by WoltLab Suite™
As a registered Member:
* You will see no Google advertising
* You can translate posts into your local language
* You can ask questions or help the community with your knowledge
* You can thank the authors for their help
* You can receive notifications of replies or new topics on request
* We do not sell your data - we promise

JOIN OUR GREAT ROBOTICS COMMUNITY.
Don’t have an account yet? Register yourself now and be a part of our community!
Register Yourself Lost Password
Robotforum - Support and discussion community for industrial robots and cobots in the WSC-Connect App on Google Play
Robotforum - Support and discussion community for industrial robots and cobots in the WSC-Connect App on the App Store
Download