Turning the key for mode exchange without teach pendant
  • Dear forum members,
    Is there a way to "hack" the KRC in order to allow switching between control modes without the teach pendant? Maybe using external PLC for that?
    We have the KRC4 compact controller and for some reason after power fault (not related to the robot, power supply was cut due to some reason) the robot from time to time changed mode from EXT to T1. Since we do not work with the teach pendant and the access to the robot is limited, we wish to be able to switch back to EXT mode without reconnecting the teach pendant, which is later disconnected and robot needs to be restarted in order to work again without teach pendant.
    There are 8 cables for the teach pendant - 2 for power, 2 apparently for the E-button ?(X40 on the board) and 4 for network connection (X42).
    Is the signal for the manual key rotation sent as a network packet? is there a way to send it via the maintenance network connection instead of the teach pendant?
    I sincerely appreciate any assistance.
    Thank you for your time.
    Best regards,
    Avi
  • Avi
    Changed the title of the thread from “Turning the key for mode exchange without teach pedant” to “Turning the key for mode exchange without teach pendant”.
  • >> Is there a way to "hack" the KRC in order to allow switching between control modes without the teach pendant? Maybe using external PLC for that?
    Probably, after all this is something created by humans, not passed down from some alien civilisation. Someone did some pretty interesting things with stuxnet too...
    Question is is this is reasonable or worth the effort...
    Are you maintaining your robot? Are batteries connected and in good shape? What is the KSS version? Did you send KRCDiag to Kuka Support to check it out?
    not exactly , there is one cable to smartPad and it has eight conductors:
    two of them are power (X306)
    two of them are circuit telling if smartPad is connected (X407)
    and the remaining 4 are EtherCat (X42, KSB)
    all signals are exchanged over the EtherCat (KSB). This includes any information displayed on smartPad, data services for USB port(s), safety signals for EStop, enabling switch, mode selector switch, etc. replicating this using some hack is very likely to be a daunting task, as everything here is proprietery (not disclosed) and reverse engineering would require skills (a lot of specialized knowledge) and possibly luck.
    Hence practical solution is to not disconnect smartPad or ... keep connecting it as needed.
  • Hello Avi!
    Did you have any success on finding out how to swap modes without smartpad? I have a similar issue and am also trying to find a way to change modes remotely!
    Best regards,