How to Change IRC 5 Main Drive Unit

  • Hello to everyone. My IRC 5 Controller is giving DC Link Voltage Very Low Alert. And I want to Replace the Main Drive Unit.

    What should I be aware of when changing the unit.

    For example, Calibration is broken? or software problems occur, is there anything I need to re-install?

  • Exercise all necessary precautions for dealing with high voltage. Power down and lock out energy source. Use a matching drive system, the newest is 09 I think and older is 04 or 05. Put the robot at the zero position if you can so that you can update rev counters when finished, if necessary. Should not have to reinstall anything if done right. It might want to update the firmware, but the main computer will figure that out.