XMOVE with OR operator
  • Hello,
    You can use a WHILE loop having that connditions or create a background program.
    For the WHILE loop, the robot will go to the final point and the motion it will be intrerupted by the conditions from the while.
    cond = 0
    LMOVE p1
    WHILE cond==0 DO
    IF SIG(1001) AND cond ==0 THEN
    BRAKE
    cond = 1
    END
    IF SIG(1002) AND cond==0 THEN
    BRAKE
    cond = 2
    END
    IF DISTANCE(HERE,DEST)<=5 AND cond==0 THEN
    cond = 3
    END
    END
    CASE cond OF
    VALUE 1:
    TYPE "Robot stopped by 1001 signal"
    VALUE 2:
    TYPE "Robot stopped by 1002 signal"
    VALUE 3:
    TYPE "Robot reached the final position"
    ANY :
    TYPE "State unkown"
    HALT
    END
    And for the backgroup program:
    .PROGRAM autostart.pc ()
    loop:
    IF SIG(1001) OR SIG(1002) THEN
    SIGNAL 2001
    ELSE
    SIGNAL -2001
    END
    TWAIT 0.1
    GOTO loop
    Use XMOVE TILL 2001
    I know that the XMOVE function had some bugs with the old AS version, make sure to have the lastest version from AS and SV. And also make sure to have a watchdog for the background program, If it is in stopped mode, the robot might collide or do other silly thing.
  • Welcome to the forum...………:beerchug:
    I have never tried using multiple signals, so cannot be sure if it will accept the syntax or not.
    However, I am pretty sure you can only detect on single signal as there are positive/trailing edge detection modes and also /ERR and /LVL options associated with the command. and these would not be possible across more than one signal.
    In which case, a background task to provide the detection signal would be an alternative.
    - but the background task must be running prior to the XMOVE instruction
  • Hello, thank you for reply
    I made like that yesterday.
    Today, I tested and everything working good with background logic. I put on the beginning program PCEXECUTE command with this logic and everything is OK.
  • Before the XMOVE function you can check if the autostart is still running:
    IF TASK(1003)<>1 THEN
    PCABORT 3:
    PCEXECUTE 3:
    END
    This code will check if the autostart3 is not running, it will execute again. If you have a different program name, you can put the name into after the pcexecute 3: program_name.