  • Hi everyone,


    I have a SmartArc loaded Comau Robot. Control Unit of Robot is Nort American version.I run weld process by pressing T1P button and Weld button (Right Menu) in T1 Mode.But I can not pressing Weld button in Remote mode. So, I can not run welding process. Can you help me ?

  • Because you must setup it in I/O Map in application section there is something lire dry run etc usually we give them some $din and in these inputs connect 24v permanently .. when it will be right you dont must press it at all..

  • Hi, the signal that must be activated is Process YES command. This signal corresponds to $IN412. There is a Application page in IO_MAP, there you select Direction-->Output and the set the Process Yes command to an input comming from PLC already mapped before.

    Then you use this signal to enable/disable dry runs from the hmi, and the check for errors by operators, for instance.