Separate thread for different issue involving the S52 controller set up.
I am attempting to perform two tasks. The first being servo gun tip force adjustment. I believe I am following the directions correctly.
I go to the force adjustment screen, scroll to set 1 insert 1000 N, deadman/enable/clamp, record force of 980 N in measured column, current calc., complete. I go to record for 2000N, I type 2000 in the set column, enter, deadman/enable/clamp, but i only get 980 N. Unless I go to the servo weld gun condition screen, and adjust my teach force to 2000 N am I able to get a higher force when in the tip force adjustment screen. I should not have to go back and forth between these two screens and change the teaching force should I?
Second task, I am attempted to program a weld...
1. I attach the weld gun, gun status 4,1, deadman/clamp/gun status. The gun connects fine
2. Program a simple open position record,
3. Deadman/enable/clamp. Gun closed, record position. Open gun, record position.
When I attempt to run the program, I get weld schedule setting data is abnormal.
If I record the step 2 with a gun status of K (workless reference). The program runs.