Still the same errors. I don't know if anyone change dip sw position but probably not.
Reinitialize Robot FS006L C with controller D71F-F00 whitout any date sheets
- okiikoful
- Thread is Unresolved
Even after rebooting?
unfortunately yes
Try ZROBOT again with the following:
10: FS Series
5: FS006L-A001
No. axes leave the same
Serial No. leave the same
I can't put "5" - Arm data is not found
Strange...………….
OK, ZROBOT again with:
10: FS Series
91: FS006L-B001
Turn off controller, then set S2 dipswitches on 1RB board same as they are now, but toggle them as they may have dust.
Do same for other dipswitches aswell and reboot again.
OK
It looks like these settings are working. Right now previous erros was missing and I have one error - D1010 Regenerative resistor overheat.
So right now I have a dip sw 2 as the begining and Robot as 91: FS006L-B001
So what are S2 settings as then, I'm confused?
Sorry for that -
I didn't change the position of sw2 so:
1 OFF, 2 ON, 3 OFF, 4,5,6,7,8 ON
That error is probably because you have fan connection missing (because you have side plate off).
Please power off and then connect, then power on again....X207 connection.
I have document for 1RB S2 settings, that are confusing and from picture of 1RB, difficult to see settings.
But they are correct yes...….
Are you error free yet?
OK right now looks everythink ok. what I have do next ? zeroing axis ?
Heehee…..finally.....good job my friend and thankyou for your patience.
Yes, zeroing is required.
However, current joint angles may not permit you to move the joints in the correct directions so:
1. Goto Aux 0503 and set ALL joints to 0 degrees.
2. Goto Aux 0501 and set ALL joints to 0 degrees.
Then make sure arm cannot fall over (I assume it is bolted down or secured).
- Make sure EMG Stops released.
- Turn Teach Lock ON on teach pendant.
- Turn Teach Switch on Controller to teach.
- Press Motor Power button (should light up and remain on).
- Squeeze deadmans to middle position, brakes should release.
- Select JOINT mode and then align all joints with scribe lines on robot (points directly up).
- Carry out Aux 0503 again ALL joints to 0 degrees and then AUX 0501 ALL joints to 0 degrees
Thank you very much kwakisaki for your help.
Everything looks good.
Good job............…
I take it you zero'd it all up fine and it's all operating error free now then?
Also, I noticed on your picture, you have 2 IO boards installed, the configuration you have at the moment will only be using the 1st one.
Do you intend to use the other one?
Yes - after zeroing no errors occurred.
Right now I will be use only one of them but if you are be able to write how can I change configuration to use both of them I will be grateful.
Yes, when you get the next opportunity:
1. Turn off the controller.
2. Remove both the IO boards.
- On the boards locate jumper J2 - near the back edge.
- This jumper sets the address of the boards, each board has 32 inputs and 32 outputs.
- 1st board J2 should be set to 1-32.
- 2nd board J2 should be set to 33-64.
3. Place them back in.
4. Power the Controller up.
5. Goto Aux 0611.
6. There change the total inputs and outputs to 64.
You should then have the full compliment of both IO boards to use then.
(it is probable that the J2 jumper is already set correctly, but worth checking/confirming first)
To add, you are more than likely using PNP IO boards too.
Attached is the External IO Manual, which contains references to the correct wiring configurations - follow 1HW references, not 1GW.