Our system is KRC4 8.5.7 HF1 and KR 90 R3100 extra HA.
The robot will be mounted on a linear track, that is kinematically integrated.
I should want a signal that my robotaxes are within a certain range, as is for the homepos, but not
evaluating the external axis. If the six robotaxes are within a parametrised range the bit should be true, no matter where the linear track is.
This could be solved by configuring axisworkspaces. The only thing that I dislike here is that for the external axes you can only set the ranges to maximum of
software limit switches. Normally axes should stop when reaching the software limit, but I suppose it is not impossible that the actual position is slightly higher then the software limit.
In that case my statusbit would never become high.
Alternative could also be a program in the submit interpreter.
Homeposition only for robotaxes
- Plc_User
Wouldn't it be the case of editing the machine data of the external kinematic in WoV and setting very high tolerance for E1's home position?
Yes, that seems to be the solution.
...I don't. You will not have a problem. You can't teach a position on the software limits. It might be possible if there are calculated positions, but then You can substract 0.1mm from limit an will not have a problem.