I am using ABB IRB 4600 robot with IRC5 Controller and I am having issue with the state of the Local IO.I have configured one IO please look that into the attached screenshot.The output state is changing when I release the dead man switch.Any suggestions in this matter would be really appreciated.
Thank you

Output states are changing when releasing deadman switch
-
robomaniac -
October 30, 2018 at 4:48 PM -
Thread is Resolved
-
-
What unit is the signal assigned to?
-
Its the local Io ,One that comes with the robot.
-
I don't think you can change this signal. Most factory signal are assigned to PANEL and DRV_1. How are you trying to use this signal. Maybe there is another way to fix your issue.
-
I am trying to operate gripper using that signal.I am creating programs for from the scratch the first time So,I don't know that its possible or not.
-
Do you have DSQ652 deviceNet on this robot? I would set up my gripper this way.
-
Can you post your eio.cfg file ?
(make a backup, look in the syspar directory)