Hello everyone,
I want to controlling UOP signal,I can change Register but i cant change UOP signal for the starting robot.
I used Proface with Ethernet(TCP), GE Intelligent Platforms.
Someone said me "controlling UOP Input signal it must start after Q6000" I tried it but it wasnt happened.
Maybe i need some configuration with SNPX_ASNG .
Proface HMI controlling UOP signal
-
fatal546 -
July 25, 2018 at 9:51 AM -
Thread is marked as Resolved.
-
-
UI start at Q6001
UO start at I6001Do you have the UI's enable in the config menu? Line 7
Do you have the REmote/local setup as Remote in the config? Line 42
What are you doing with the HMI?
-
First of all thank you for your reply,
I fixed my problem right now. The problem was rack number of UI signal, When i change the number of 34 (Flag).It was solved -