Fault reset by push button
  • NovaFlatline
  • May 27, 2018 at 5:54 PM
  • NovaFlatline
    31
    I'm new to fanuc, new to maintenance position. I have the ability to learn quickly. Forgive me if my terminology is off. I learned how to setup and program a rj3b controller connected to a r2000 165f
    I'm having trouble with reseting the fence fault. That is generated by openimg the fence. I figured out to to simultaneously trigger both the chains so I don't get the chain fault. My problem is that I can not reset the controller with a push button wired to a input on the supplied plc rack.
    What is the correct "mapping" or "wiring" that I would have to follow to remotely reset the fault?
  • Ninad Joshi
    44
    • May 29, 2018 at 10:23 AM
    What type of interfacing is done between PLC and robot? Is it hard-wired or any communication protocol is defined like EthernetIP or Profinet?
    Get your fault reset push button input to PLC first and then (if robot and plc IOs are properly mapped) program this PLC input to robot UI 05(Reset) in peripheral inputs of robot. Check the status of UI05 input by pressing the fault reset PB.
  • NovaFlatline
    31
    • May 29, 2018 at 3:35 PM
    I am using supplied 24 Vdc positive and negative wired appropriately.i have the push button wired directly to the plc rack in the controller. I do not know how to map the plc input to the UI 05.
  • HawkME
    568
    10
    3,268
    • May 29, 2018 at 4:19 PM
    You say the "PLC rack in the controller". That sentence doesn't make very much sense. The robot controller is not a PLC. It may or may not have a rack of I/O cards. A PLC would be a separate device unrelated to the robot, that may or may not have its own I/O cards.
    So which is it? Do you have a 3rd party PLC with a rack of I/O cards or do you have Fanuc I/O cards?
  • NovaFlatline
    31
    • May 29, 2018 at 7:03 PM
    Digital input and output cards located inside the controller that fanuc provided. example DI 1is my push button. How do I map the DI 01 to UI 05.
  • HawkME
    568
    10
    3,268
    • May 29, 2018 at 7:07 PM
    Well if your DI's are already mapped, then all you have to do is look at the mapping for that DI and copy the same mapping to UI[5], i.e., make UI[5] the same rack/slot/start point as the DI that you want it to match.
  • NovaFlatline
    31
    • June 4, 2018 at 4:35 PM
    DI's are not mapped. How do I map them. Again forgive me, as I am self taught on this controller.
    DI 01: when I veiw it from the I/O screen, I can see it go on and off when I push the button.
    I can view the UI as well. I am confused on how to call them, or map them to each other.
  • stare284
    24
    373
    • June 4, 2018 at 5:35 PM
    On the DI screen push config and it will show you the configuration for the inputs.
    Then in the UI screen set the config to the same as the DI for the input you need.
    Example
    Rest Push button is DI1
    Rack Slot Start PT
    DI 1-16 89 1 1
    Then you would set the UI as follows
    UI 1-4 0 0 0
    UI 5-5 89 1 1
  • stare284
    24
    373
    • June 4, 2018 at 5:42 PM
    Here is another example with DI15 being the reset button.
    Images
      • 45.14 kB
      • 587 × 322
      • 41
      • 46.14 kB
      • 554 × 258
      • 31
    Files
    UI.JPG_thumb 19.35 kB – 272 Downloads DI.JPG_thumb 19.02 kB – 267 Downloads
  • NovaFlatline
    31
    • June 5, 2018 at 3:59 PM
    Thank you!!
  • NovaFlatline
    31
    • June 5, 2018 at 4:37 PM
    • #11
    Reset now works, however new problem SRVO-037 IMSTP input do I need those to be mapped to something?
  • HawkME
    568
    10
    3,268
    • June 5, 2018 at 4:39 PM
    • #12
    Yes, UI 1,2,3 & 8 all need to be on in order to allow the robot to run when UI signals are enabled. You can read about this in the manual by searching for UOP Input Signals.