Cabinet krc2 doesn't hibernate
  • jesusvaricap
  • December 6, 2017 at 6:01 PM
  • jesusvaricap
    259
    Hello ,
    KRC2 KR2210_L150
    KSS 5.2.14
    The problem its the next: when the cabinet shutdown doesn't hibernate black screen intermediately and start cold , also at turn on its necessary to mastering all axis
    Usually the problem solves changing batteries or the fuse corresponding to the batteries charging, all mentioned before was checked, also the black module siemens was checked the presets on it was not alteraded , and the led green its active.
    There is installed a HDD 8GB , solid state IDE partitioned (C:\ 1.99Gb, D\:5.62Gb) Now, about the C:\ partition its full! ??? maybe the full partition its the problem , but i have not a lot programs , maybe there is a lot trash system.
    How can i solve it?
    what files or folders i need to clean ?
    it a software / hardware problem ?
    pictures and backup attached
    thanks
    Images
      • 144.54 kB
      • 675 × 900
      • 30
      • 168.84 kB
      • 675 × 900
      • 17
    Files
    IMG_9513.JPG_thumb 30.19 kB – 66 Downloads IMG_9514.JPG_thumb 30.75 kB – 65 Downloads archive.zip 876.81 kB – 12 Downloads
  • the leg
    643
    • December 6, 2017 at 7:00 PM
    Is the charge circuit working have you metered it ? are the batteries ok ?
    it could be the KPS600 isnt allowing the charge circuit so you would need a new KPS600 ( G1 )
  • jesusvaricap
    259
    • December 6, 2017 at 7:04 PM
    the batteries are new , how can i check charge circuit ?
  • the leg
    643
    • December 6, 2017 at 7:08 PM
    put a meter across the cable that connects to batteries normally the outer most connectors
    disconnect the batteries and put your meter across the cores of cable you should be getting 26V - 27 V
  • jesusvaricap
    259
    • December 6, 2017 at 7:21 PM
    i measured 1.4vcd
  • the leg
    643
    • December 6, 2017 at 7:25 PM
    1.4 volts ?
    thats not good needs to be over 24V that will be your problem
  • jesusvaricap
    259
    • December 6, 2017 at 7:26 PM
    yes , how can i detect the failure ? all fuses its ok ..
  • the leg
    643
    • December 6, 2017 at 7:43 PM
    if the power supply isn't outputting the correct voltage then it has a problem with the charge circuit and in turn the batteries can not sent the voltage back to keep the pc powered up while it shuts down new G1 i am afraid
  • jesusvaricap
    259
    • December 6, 2017 at 7:53 PM
    from G2 power suply left cabinet are 27v , maybe the problem its the KPS G1 , in two days i can do a swapping.
    any other advice ?
  • the leg
    643
    • December 6, 2017 at 11:08 PM
    i said G1 not G2
  • robot-cnc
    431
    • December 7, 2017 at 11:30 AM
    • #11
    if you need a KPS 600 /20- ESC alias G1 unit I can provide one. art. no. 00-111-846.
    Images
      • 3.55 MB
      • 4,032 × 3,024
      • 37
    Files
    20171127_215905.jpg_thumb 24.13 kB – 84 Downloads
  • the leg
    643
    • December 7, 2017 at 7:08 PM
    • #12
    i also have 00-115-115 G1s in stock :top:
  • jesusvaricap
    259
    • December 8, 2017 at 5:26 PM
    • #13
    thanks for your reply, send me a message with your offer $
  • jesusvaricap
    259
    • January 26, 2018 at 1:02 AM
    • #14
    Hello ,
    I do a swapping from other robot , and work correctly , the cabinet hibernate, but few days later the same problem again.
    The other KPS "damaged " work correctly on other robot.
    the module siemens appears green led , the batteries each one measure 12.3v , 12.8v
    maybe the RAM memory its damged ?, disk c:/ not enough free space ?
    BR
  • jesusvaricap
    259
    • February 1, 2018 at 7:11 PM
    • #15
    Problem Solved.
    the failure was the module siemens , that was very confused , because the control module works correctly ,( Green led when batteries charged ,led red when batteries discharged or not plugged).
    i do a swapping of module Siemens , and the cabinet hibernate
    :icon_smile:
Users Viewing This Thread