DX200 CC Link registers

  • If I set up the CC link module to use registers, how to i know what the corresponding registers are at my PLC ?


    EDIT: I found the registers, the PLC CC link parameters were set up for D2000, and it turns out someone was already using data in that area so i was able to confirm communication.


    New question: How can I push Register data (M022) into a Double or Integer to be used in jobs?

    Edited once, last by WattUp ().

  • Hi,
    You can use GETREG instruction. Use register number as source and INTEGER variable as destination. Only I Variable number/LI Variable number/I [Array
    number]/LI [Array number].

  • Thank you,


    I was trying to pass numbers in to become position offsets;


    I used a GETREG to move into a LI##, then a SET to get it into a D##. Then i used a SETE P## (1) D##.