DCS Errors after loading backup to Roboguide
  • romanzo
  • August 23, 2017 at 6:23 PM
  • romanzo
    21
    Hey all, I loaded a project from a backup onto roboguide and am getting a few DCS errors.
    These are the errors I am receiving:
    SRVO-409 DCS SSO Servo Disconnect 1,1
    SRVO-406 DCS SSO SVOFF input 1,1
    SRVO-408 DCS SSO Ext Emergency Stop 1,1
    Any help on getting these to go away would be much appreciated.
  • Nation
    Typical Robot Error
    552
    1,934
    • August 23, 2017 at 9:50 PM
    You will have to go into the DCS Safe I/O connections and jumper out the signals that are connected to those inputs.
    Usually it is something that looks like this:
    CSO[1] = SSI[1]
    You would just NOT the SSI signal:
    CSO[1] = !SSI[1]
  • TFROK
    14
    • August 24, 2017 at 7:32 PM
    Or just disable DCS all together. Variables - $DCS_CFG - $SYS_PARAM. If that variable is set to 0 DCS is enabled, if its set to 1 its disabled.
  • PITT-SC_Robot_Guy
    • July 1, 2022 at 5:23 PM
    make sure to cycle power and apply DCS settings for this to work.
    this worked for me. thanks TFROK