When starting production on a program I am getting the syst-014 program select failed and memo-073 program does not exist errors. When I am in the teach pendant mode I can view and step through the entire program. Therefore, it exists and runs. However, as soon as I turn off the teach pendant to start the cycle I receive these errors. Any thought what may be causing these errors?
Thanks
Syst-014 and Memo-073 alarm errors
-
toddcollins -
April 2, 2017 at 4:32 AM -
Thread is marked as Resolved.
-
-
it can be there is a program runned by pmc or bglogic or macro
-
We did a cold start and having the same issue. Wouldn't a cold stop stop
These programs? Thanks for your reply -
What is the name of your main program that you are trying to run? And no, a cold start won't stop BG logic or PMC.
Sent from my SM-G930V using Tapatalk
-
We are running PNS0001. We found out this was deleted. That is why the file could not be found. We reloaded it and now are back up and running. Thank you for all the replies.