    We we turn on our robots every morning, the "weld" is not enabled and the operator is consistently forgetting to turn this on. Is there a variable that i can change somewhere? I managed to find one for the speed but nothing for weld yet.
  • bidzej
    23
    592
    • December 14, 2016 at 3:53 PM
    create a TP program with the "Ignore pause" parameter set to ON, write a single line in there which changes the appropriate system variable and then go to CONFIG menu and set this program to be executed in Cold + Hot start.
  • ajjohns2003
    • December 14, 2016 at 5:29 PM
    Thank you for the quick reply, how would I go about writing the WELD enable into the program? Where can I find this? My Programming is pretty basic when it comes to anything other than welding and motions.
    Sent from my SM-N920W8 using Tapatalk
  • bidzej
    23
    592
    • December 14, 2016 at 7:50 PM
    1. Create a program, give it a name, go to DETAILS, set Ignore pause to ON. Also, be sure NOT to assign any motion groups to this program (Group mask set to [*,*,*,*,*,*]).
    2. Write the following line in the program
    $AWEPOR[1].$ARC_ENABLE=1
    Hopefully that is the variable's name for your R-J3, this comes from the R-30iB as far as I remember. If not, then try searching for a similar name in the $AWEPOR structure or some other $AW* structures.
    3. Go to Menu -> System -> Config and put the name of your new program in the fields for automatic program execution on Hot- and Cold Start.
    4. Done.
    You can use the very same program to set many other parameters that you want to set on startup (other system variables, DOs, Registers etc.) - just add anything you need to the code.
  • ajjohns2003
    • December 14, 2016 at 8:09 PM
    Thank you again for the information. Is there an option to write this as code or is it an instruction? That's where I'm stuck at the moment.
  • bidzej
    23
    592
    • December 15, 2016 at 8:33 AM
    1. Go to program editor, then use [INST] -> Miscellaneous -> Parameter name -> $... = ...
    2. Select the first "..." with the cursor, press Enter, type AWEPOR[1].$ARC_ENABLE
    3. Select the second "..." with the cursor, press enter, select Constant, type 1.
  • ajjohns2003
    • December 15, 2016 at 2:14 PM