Hi Paavo,
did you get it working? It would be nice if you could provide some feedback.
I will probably get a similar gripper for an iiwa and I am using the media flange pneumatic.
You seem to have the IO pneumatic flange, right? So why do you have so much additional hardware (Beckhoff EK1100 ...)?
The manual states that: "The media flange IO pneumatic is supplied with power by the robot
controller. No external power or data source is required. Data cable
X650, X651 is required for operation."
Please correct me if I am wrong. I just want to get a general idea.
Thank you.
We have now built a "custom construction" at the flange of iiwa (See photo) . We extract power from X11, X12 and X13 sockets of the flange for Schunk EGL 90 PB (the gripper) and for the Beckhoff EK1100.
I have tried to configure the connection to the gripper in WorkVisual. I have managed to connect EK1100 and EL6731 to the KUKA System bus. I have .gsd-file of the EGL 90 Pb B gripper provided by Schunk. I have inserted this .gsd-file to the Profibus IO from the EL6731 in WorkVisual (EL6731 is profibus master and gripper is slave). The screenshot (attached) clarifies the situation in WorkVisual.
If I export this configuration to Sunrise project and deploy the project from Workbench to the to the controller, the following error appear on SmartPAD: <SYS-X48> Error during ECat stack initialization. Device: EL6731 PROFIBUS DP Master [Init: init command failed - PREOP to SAFEOP]."
It is well possible that I have not configured the the settings in WorkVisual correctly. (eg. distributed clock settings of EL6731). If some obvious reason for the above error can be spotted based on the attached WorkVisual-screenshot, please let me know.