Resolver problem
  • ezzine
  • July 14, 2016 at 3:16 PM
  • ezzine
    21
    • September 1, 2016 at 5:38 PM
    • #21
    what should i write in MODULE case
  • panic mode
    1,300
    13,144
    • September 1, 2016 at 5:55 PM
    • #22
    nothing... (normally).
    (there is a longer explanation but for that please consider Kuka training).
  • ezzine
    21
    • September 1, 2016 at 6:07 PM
    • #23
    i'm unable to do a kuka training ... so can you help me please ?? as i said i've wrote $MEAS_PULSE[] and nothing appeared all it says ''''' what could be the problem??
  • panic mode
    1,300
    13,144
    • September 1, 2016 at 9:04 PM
    • #24
    if you see empty string as a result and there is no message about missing object, you are using correct name, variable is declared, but not initialized (there is nothing updating the variable). are you sure you activated fast measure inputs in WoV? did you deploy and activate the project after that?
    it is under Additional Controller Settings, Enable Fast measurechannels
  • ezzine
    21
    • September 1, 2016 at 10:30 PM
    • #25
    yes i'm sure about it ,,,can i check it with the smart pad ?? i forgot to mention that i'm working with WoV 4.0 now
  • panic mode
    1,300
    13,144
    • September 5, 2016 at 7:35 PM
    • #26
    if the configuration is correct (even without X33 interface installed in the cabinet), you should be able to to monitor high speed inputs with single variable monitor