I have problem in define WAGO 750-306 ; I change IOsys.ini signal LED connect is on but input & output miss .
I do reset I/O configure but MFC driver and Device net have error
please
error on writing , driver .DN2DRV
- km427
- Thread is marked as Resolved.
-
-
-
in IOsys .ini
If define
DEVNET=2,dnInit,dn2drv.o
I have erroe on writing , driver.dn2drv and LED signal connect on WAGO is ON , but input and output haven't in monitor digital input OR digital out put
but If define
DEVNET=2,dnInit,dndrv.o
I don't have error ,but LED signal connect on WAGO is off
what do I do ?
please help me -
-
Km427
In the [DEVNET] section make sure the inputs and out puts are defined correctly
example
[DEVNET]OUTW0=3,0,x1 ;$OUT[1-16]
INW0=3,0,x1 ;$IN[1-16]outw = the outputs are addressed as a word
0 = start at the first output address in the kuka outputs address = x*8+1 ed OutW2 would start writing 16 bits at $OUT[17]
3 = the MAC ID of the 750-306 set by the first 6 dip switch
0 = where to read the data from the 306
x1 = not really sure about that one in the book it says "The multiplier is used to define the address range width of
the connected devices (multiplier value 1, 2, 3, ...) to allow
a possible subsequent address expansion"
I would just leave it at x1also use DEVNET=2,dnInit,dn2drv.o
I am pretty sure support for dndrv.o was discontinued a while back but that would depend on the age of your robot.
one other thing that has bit me in the rear is that if you use multiple nodes in the devnet.ini file they need to be called from low to high
eg
this is good[krc]
debug=0
baudrate=5
LOGFILE=1
[1]
Macid=3
[2]
Macid=5this is no Good
[krc]
debug=0
baudrate=5
LOGFILE=1
[1]
Macid=5
[2]
Macid=3 -
hi
Our friend
Thank you for help me , solved the problem .