when are the servo drives engaged?
  • BluesMatt
  • May 13, 2016 at 2:30 PM
  • BluesMatt
    176
    I'm looking for a $OUT[xx] that indicates when the servo drives are on or off. I found $OUT[1011], it is labeled as SYS, and appears to go on/off when engaging the drives on/off using the SmartPad. The same is true for $OUT[1015]. I need this because I need to turn an indicator light on/off on my HMI screen when the drives are on/off.
    Are either of these outputs an appropriate one to use?
    Which $OUT[xx] is used to pull the contactors in?
    Building robotic welding systems.
  • s2007.ravi
    14
    585
    • May 13, 2016 at 2:44 PM
    Look into STEU>MADA>Machine.dat and you should look for an output saying $DRIVES_ON and see which output number is assigned to this system tag. It will give you exactly when the drives are engaged.
    Also, you can look for $DRIVES_OFF which will be ON when the motors are not engaged.
    Edited once, last by RS (May 13, 2016 at 2:46 PM).
    panic mode
    1,280
    13,085
    • May 13, 2016 at 3:23 PM
    those would be inputs to power on/off drives from another controller.
    to see which output is used to indicate that robot drives are on, check R1\STEU\MADA\$Machine.dat
    there should be line like
    SIGNAL $PERI_RDY $OUT[999]
  • BluesMatt
    176
    • May 13, 2016 at 4:28 PM
    Looking in $machine.dat, I see 4 outputs that seem relevant:
    $STOPMESS $OUT[1010] <-- goes OFF when drives are engaged using the SmartPad
    $USER_SAF $OUT[1011] <-- goes ON/OFF when drives are engaged/disengaged using the SmartPad
    $PERI_RDY $OUT[1012] <-- not changing as I engage / disengage the drives using the SmartPad
    $SPOC_MOTION_ENABLE $OUT[1015] <--goes ON/OFF when drives are engaged/disengaged using the SmartPad
    $STOPMESS appears to go ON after an error occurs that stops the robot
    The other 3 are not in my copy of the System Variable pdf.
    From the names, it seems like [1015] is the one to use, but I'm not sure. Would this output ever incorrectly represent the status of the drives?
    panic mode
    1,280
    13,085
    • May 13, 2016 at 5:52 PM
    read system integrator or system variables manual (not just the latest one, also check KRC2 documentation !)
    section on AutoExternal in SI should cover it all...
    Images
      • 13.82 kB
      • 449 × 154
      • 33
    Files
    Peri_rdy.jpg_thumb 9.24 kB – 16 Downloads
    Edited once, last by panic mode (May 13, 2016 at 5:58 PM).
  • the leg
    643
    • May 13, 2016 at 6:48 PM
    on a krc4 you can use $could_start_motion this replaces the $pri_rdy of the krc2
Users Viewing This Thread
  • 1 Guest