vkrc2 krc 4.1.6 cannot jog/master
  • uberdoom
  • April 8, 2016 at 4:10 AM
  • uberdoom
    97
    Hey All,
    Looking for a little guidance here. I know there have been a few posts on here regarding this, but I cannot find how people diagnosed the problem:
    Controller turns on fine and boots up. Proper changes have been made to allow for motion and the such including the GM safety bypass plug properly jumpered. All of this is done in T1 mode as an expert user. The control cabinet is a GM vkrc2 circa 2003 running on krc 4.1.6.
    I pull the deadman switch (yes halfway), wait for drives, and when I go to jog the robot...error city.
    It "usually" goes like this:
    1245 quit servo bus disturbance DSE 1
    1216 ackn drives error A1-6 No. TRIP
    and sometimes it throws
    1229 Ackn watchdog power module PM1
    and some others related to power module every so often related to low voltage of pm1.
    No communication errors or anything...
    I thought it might be the cable from DSE to KPS, but when I pull that it throws different errors.
    Any way to diagnose the power module simply or suggestions on best place to start? I should also add this robot was delivered missing the mfc/dse card and that they were replaced from a different robot. I'm wondering if that couldn't have something to do with this. Thanks.
    DJ
    Images
      • 3.32 MB
      • 4,032 × 3,024
      • 37
      • 2.25 MB
      • 4,032 × 3,024
      • 61
      • 1.16 MB
      • 4,032 × 3,024
      • 57
      • 3.6 MB
      • 4,032 × 3,024
      • 62
    Files
    IMG_9702.JPG_thumb 29.79 kB – 167 Downloads IMG_9703.JPG_thumb 30.95 kB – 165 Downloads IMG_9693.JPG_thumb 37.13 kB – 163 Downloads IMG_9705.JPG_thumb 37.93 kB – 161 Downloads
  • uberdoom
    97
    • April 8, 2016 at 2:09 PM
    I forgot to mention two more things:
    1. Both red and green light are on and constant on the RDW card.
    2. Under ESC monitor I get -->
    Fatal error execution terminated
    ESCInternalERR13
    Possible reason: missing power supply or ESC hardware defect.
    panic mode
    1,296
    13,137
    • April 8, 2016 at 7:44 PM
    if you get diagnostics point at ESC internal error, ESC replacement is the best thing you can try next.
  • uberdoom
    97
    • April 9, 2016 at 8:55 PM
    The gm cabinets don't have typical krc2 ESC board now ESC connector from kps600 as seen in my photos above. On the wiring diagrams provided with bot I don't see any reference to ESC relays.
    Anyone with a gm vkrc2 care to clue me in? This is a kr200 arm. Thanks.
  • uberdoom
    97
    • April 12, 2016 at 6:11 AM
    That is...there's no ESC board nor x14 connector from the KPS600 to the non-existent ESC board. There is the CC1 plug to the fe207/208 boards.
    Can anyone with a GM vkrc2 run MONITOR --> DIAGNOSIS --> SECURITYCIRCUIT and take a picture of what they see? I would greatly appreciate it.
    When I run the DSE/RDW/MFC TOOL and go to drivebus diagnostic menu I can monitor voltage of the intermediate circuit with deadman engaged and off. I have about 575V at KSP and KSD 1-6 with deadman engaged. All drives are "ok". So, I'm ruling out needing to replace the KPS600. I have attached an image of the MFC display register. Again, I'm not sure what normal on this should be. Any input would be of great help.
    The fault code that I'm getting after activating drives is 1245 quit servo disturbance DSE1. I'm just trying to piece together where this could be coming from. Green LED is blinking on the DSE, as noted, there is communication between DSE and RDW. I have power at the KPS and all KSDs. Seems to be something in the security circuitry. But I'm not getting any errors that are indicating what exactly. DSE and and MFC were replacements from another bot...do I need to sink DSE MFC and RDW?
    I activate drives with the deadman switch, go to jog, and receives errors (after voltage is present). The top green light on the KPS600 goes from blinking green to constant green (indicating proper voltage) but the bank of 4 leds (2 green 2 red) never light up. $GM_WO_PLC set to true, MOVE_ENABLE at 1025, LPDN scanner commented out.
    I have attached pertinent pictures of screenshots including a layout of my cell i/o. Thanks to anyone reading this and giving any amount of brain waves.
    DJ
    Images
      • 203.39 kB
      • 720 × 540
      • 32
      • 200.77 kB
      • 720 × 540
      • 31
      • 222.74 kB
      • 720 × 540
      • 55
      • 196.85 kB
      • 720 × 540
      • 52
      • 226.56 kB
      • 720 × 540
      • 44
      • 250.06 kB
      • 720 × 540
      • 40
      • 216.09 kB
      • 720 × 540
      • 35
    Files
    IMG_9784.jpg_thumb 31.13 kB – 157 Downloads IMG_9785.jpg_thumb 31.75 kB – 155 Downloads IMG_9774.jpg_thumb 34.7 kB – 153 Downloads IMG_9775.jpg_thumb 32.03 kB – 153 Downloads IMG_9776.jpg_thumb 34.29 kB – 150 Downloads IMG_9777.jpg_thumb 35.11 kB – 150 Downloads IMG_9783.jpg_thumb 31.77 kB – 149 Downloads
  • uberdoom
    97
    • April 12, 2016 at 6:17 AM
    Forgot one...
    Images
      • 215.86 kB
      • 720 × 540
      • 45
    Files
    IMG_9667.jpg_thumb 30.02 kB – 150 Downloads
  • SkyeFire
    1,060
    9,456
    • April 12, 2016 at 3:24 PM
    Okay, this is the older GM setup, pre-ESC, using the FE207 and FE208 boards with all their safety relays. You want to check both boards for red lights. IIRC, all the relays operate in triads -- two close and one opens, and all three have to actuate within ~20ms (I think) of each other or a single-channel fault occurs. The nice thing about the FE boards is that they're fully detailed in the electircal drawings, although they do take a little puzzling out.
    But the original error, where the motors come on but then the system faults as soon as you try to move, suggests that there's an issue shifting from the intermediate circuit. Is the K1 relay closing?
  • uberdoom
    97
    • April 12, 2016 at 4:14 PM
    Thanks skyefire. By the k1 you are referring to the g1/k1 on the kps600? If so then yes. When I monitor the kps voltage it goes from 23v to 575v after pulling the deadman switch. This happens after k1 closes.
  • SkyeFire
    1,060
    9,456
    • April 12, 2016 at 10:44 PM
    Hm... given that lack of error messages before you try to jog, and the fact that K1 appears to close properly, my suspicion is the PM1 module.
  • uberdoom
    97
    • April 12, 2016 at 11:00 PM
    It does throw pm1 under voltage and watchdog pm1 errors sometimes. I'll get the codes when I'm back by the bot later and post pics.
    Any way to troubleshoot that?
    Thanks again.
  • uberdoom
    97
    • April 12, 2016 at 11:17 PM
    • #11
    1223 ackn under voltage pm1
    1201 quit buffer battery voltage low pm1
    1229 ackn watchdog power module pm1
    I only get these when trying to jog the robot.
    When I open the master dialogue and try to jog I don't get them.
    I did install new batteries.
  • uberdoom
    97
    • April 13, 2016 at 5:10 AM
    • #12
    In regard to tracing down leds on the fe207/208:
    Number one:
    6k2 on fe207. Associated led is dark (v54) traces back x807 pin 30 on MFC. drives on MFC.
    I've attached a picture of it and the wiring.
    Please see picture of MFC input register. 1st pic is without deadman. 2nd is with it pulled. Where can I find the register output code meaning?
    Number 2:
    8k1 8k2 8k3 on fe208. 1 and 2 are not lit up and 3 is red. I've attached picture with wiring. These are for external auto stop so doesn't seem pertinent.
    I've been reading over this post: https://www.robot-forum.com/robotforum/kuk…-help-urgently/
    Seems like it could be power module, rdw, dse, kps, cables, ksds...I think I've narrowed the field a bit.
    Images
      • 129.53 kB
      • 450 × 600
      • 57
      • 78.31 kB
      • 450 × 600
      • 57
      • 209.28 kB
      • 720 × 540
      • 40
      • 191 kB
      • 720 × 540
      • 23
      • 181.52 kB
      • 720 × 540
      • 44
      • 121.58 kB
      • 720 × 540
      • 37
    Files
    IMG_9815.jpg_thumb 22.31 kB – 148 Downloads IMG_9814.jpg_thumb 37.91 kB – 149 Downloads IMG_9810.jpg_thumb 32.33 kB – 150 Downloads IMG_9811.jpg_thumb 31.45 kB – 151 Downloads IMG_9808.jpg_thumb 36.65 kB – 147 Downloads IMG_9809.jpg_thumb 24.82 kB – 145 Downloads
  • uberdoom
    97
    • April 13, 2016 at 3:13 PM
    • #13
    Skyefire...by power module you are referring to the KPS600, correct?
    Like I said, I do get voltage at the KPS but my guess is this has something to do with the internal logic. There are two banks of LEDs on it. The top being one red and one green. Red does not light up (except on boot up) and green blinks until K1 closes and then is constant green until voltage goes back down. The other bank, two red two green, never lights up. No blinking, no anything.
    panic mode
    1,296
    13,137
    • April 13, 2016 at 3:39 PM
    • #14
    top two LEDs work as expected,
    bottom two red LEDs are the issue, they should be both flashing fast. any time they are solid (in any state), something is wrong.
    this looks like internal fault.
  • uberdoom
    97
    • April 13, 2016 at 3:43 PM
    • #15
    Thanks PanicMode.
    I just want to clarify that KPS600 and PM1 are in fact referring to the same thing...
    panic mode
    1,296
    13,137
    • April 13, 2016 at 6:47 PM
    • #16
    yes but only when you have just one KPS600...
  • uberdoom
    97
    • April 15, 2016 at 4:15 AM
    • #17
    Caveats. Thanks for the help.
    I'm swapping it out next week. From reading all these posts seems like quit servo DSE 1 errors end up pointing back to the KPS. I'll find out soon enough.
  • uberdoom
    97
    • April 23, 2016 at 1:55 AM
    • #18
    Replaced the KPS and she moves. Thanks for all the help.
    panic mode
    1,296
    13,137
    • April 23, 2016 at 3:34 AM
    • #19
    :beerchug: