How can I Bypass External Hold Temorarily
-
ashishyadav -
December 23, 2015 at 3:43 PM -
Thread is Resolved
-
-
The external hold circuit is normally closed. So if the external hold circuit is open you can put a jumper in the circuit. I would need to know what controller you have to tell you where to start looking.
Also are you sure it's an external hold and not a hold because the PLC is not on line or a welder is not on line?
-
You can edit in LAD Editor to coil "40067" False is not holding State.