Hi
I must Connect fronius To krc4 by ethercat.
The costumer service Tell me i must Connect The coupler To x65....
But where is x65
x65 where is
- axv6l
- Thread is marked as Resolved.
-
-
it is an option. it is usually only installed if there are EtherCat I/O in the cabinet - just below door (KRC4 standard or extended) or near top on the front of KRC4 compact controller.
if there is no I/O or anything else installed on KEB (Kuka Extension Bus), just run network cable from X44 on CCU (this is KukaExtensionBus). If there is somethjing already wired to X44, follow the KEB network cable until you reach last device (it will have out connection for EtherCat, or example EK1100 when using I/O option).
-
I've EK1100 , so I must connect my coupler of the fronius in the same position X44,
-
no...
EK1100 connects to X44, Fronius connects to other Ethercat port on EK1100. Btw, if you are going this route, talk to Fronius about using "econo" version of their fieldbus kit (it is mounted not on the back side of the welder but in your robot cabinet). This will save you headacke...
-
for configuration in workvisual......in out and other......can you help me? -
i will be happy to offer help but you need to do your part (see three points at the bottom of my posts).