Transfer DCS setup from roboguide to real robot.


  • Details in DCS manual.


    DCS setting parameters are backed up in the following files.
    Most commonly, it would be DCSPOS.SV, DCSIOC.SV, and SYSVARS.SV


    DCSPOS.SV Position/Speed Check function (Includes user setting of Stop Position Prediction)


    DCSIOC.SV Safe I/O Connect function and user comments of the Safe I/O signals.


    SYSCIPS.SV DeviceNet Safety or EtherNet/IP Safety (Items in DCS CIP safety menu)
    NOTE - DCS parameters set by an external configuration tool are not included.


    SYSPASS.SV Code numbers


    SYSPNSF.SV PROFINET Safety (Items in DCS PROFINET safety menu)
    NOTE - F-Parameter is not included.


    SYSMAST.SV Mastering parameters


    SYSVARS.SV Robot setup data, Robot model, Defaults for Stop Position Prediction, Safe I/O device,
    Auxiliary axis servo off (local stop).


    LADDERS.PMC Safety PMC program.


    SYSFLSF.SV Safety function by FL-net (Items in DCS Safety function by FL-net menu)



    NOTE
    1 When DeviceNet Safety function is used, basic devicenet settings (such as Mac
    Id, baud rate) are held in SYSDNET.SV. Backup/restore SYSDNET.SV with
    SYSCIPS.SV if required.
    2 If EtherNet/IP Safety is used, standard settings such as IP address and subnet
    mask will be saved in SYSHOSV.SV. If necessary, SYSHOSV.SV must also be
    saved with SYSCIPS.SV.
    3 In both DeviceNet Safety and EtherNet/IP Safety function, the Safety PLC data
    set in the robot (eg. SNN) is not included in any application backup. It must be
    explicitly set on a robot from the Safety PLC configuration software.
    4 When PROFINET Safety function is used, basic PROFINET settings (such as
    I/O Device configuration) are held in PNIO.SV in A05B-2600-J930, or in
    PMIO.SV in A05B-2600-R834. Backup/restore PNIO.SV or PMIO.SV with
    SYSPNSF.SV if required.
    5 In PROFIsafe, F-Host is supposed to send F-Parameter to F-Device.
    F-Parameter is not stored in any application backup.
    6 When Safety function by FL-net is used, basic FL-net settings (such as area 1/2
    configuration) are held in FLNET.SV. Backup/restore FLNET.SV with
    SYSFLSF.SV if required.