Reg Robot fault SERVO 136

  • Dear Friend


    SRVO-136 DCLVAL alarm was came on 30ib robot per day 2~ 3time came , pl kindly give the countermeasure for this concern


    pl tell your experience what is the real root cause . :wallbash:

  • SRVO-136 DCLVAL alarm (Group: i Axis: j)


    (Explanation) The servo the DC current of amplifier (DC link
    voltage) of the main power supply is abnormally
    low.
    - This alarm occurred during robot operation.
    (Action 1) Check the input voltage to the controller is within
    the rated voltage and no phase is lack. And check
    the setting of the transformer is correct.
    (Action 2) It is possible that an instant disconnection of power
    source causes this alarm. Check whether an instant
    disconnection occurred.
    (Action 3) Modify the program in order that robot and the
    auxiliary axis do not accelerate simultaneously in
    the system with the auxiliary axis.
    (Action 4) Replace the E-stop unit.
    (Action 5) Replace the servo amplifier.
    - If this alarm occurred before the magnetic contactor is
    turned on:
    (Action 1) Check whether the circuit breaker in the
    emergency stop unit is OFF. If it is OFF, check the
    servo amplifier and the wiring between the servo
    amplifier and the emergency stop unit. If anything
    is abnormal, replace it. Else, turn on the breaker.
    (Action 2) Check the input voltage to the controller is within
    the rated voltage and no phase is lack. And check
    the setting of the transformer is correct.

  • Dear friend

    already checked the voltage, As per manual remedy we have confirmed the input voltage to the controller found Ok


    but issue still not closed , group-1 axis-1,2 only coming , if any body well know the reason pl let me share me..

  • Check if you have a cable to the robot that is big enough, else when the robot uses a lot of power, the voltage drops and give these kind of problems.


    And for the same reason, check if there are devices that draw a large current are on the same electrical group.
    Starting a very large electro-motor gave this fault in our factory, and an extra cable and group solved the problem.