I need to put my R-30iA mate controler away from operator, so I need to have some external buttons for cycle start and reset. How can i connect those?
greetings
Hi!
I need to put my R-30iA mate controler away from operator, so I need to have some external buttons for cycle start and reset. How can i connect those?
greetings
Thanks for answer, but still I cannot find answer how to bind i.e. DI 101(from CRMA58) to UI
No need to bind DI to UI. Simply configure your input card so that the input will be configured as UI. Use the function with user operator panel and you will have everything you need.
I don't remember how exactly is crma58 configured, but let say DI[101] is rack 65 slot 1. All you should do is to remove this config from DI and put it to UI config. Then your input from crma is joined with some UI. Does it make sense? I can take a look at config tomorrow If you will need help. Or maybe someone else can explain it better.
Tomas
Is it possible to use only a few DI's as UIs? I mean, can you use only i. e. CYCLE START and FAULT RESET mapped to DI[1] and DI[2]?
As far as I know, even when mapping a single UOP signal to a rack, slot and start pt, the controller maps the whole UOP signal set...
It's definitely possible to map only what you want. We use it. Behaviour is affected by System - Config - UOP auto assignment.
Tomas
Hi! Thanks for help.
I've managed to set my UOP start signal[UI6] to [DI 101].On config menu it should be:
[UI 6 - 6] [48] [1] [1]
But...
On I/O monitor I see on/off blinking on that UI input when I'm pressing this button, but in Auto mode nothing is happening. Not even a error code is shown. It just wont start the robot. Anyone knows why?
thanks
I have no idea how much you know about UOP, so I will try to describe it in more detail:
1) You should have UOP signals enabled (MENU/SYSTEM/CONFIG/Enable UI signals - True
2) Remote / Local setup must be set to Remote ((MENU/SYSTEM/CONFIG/Remote / Local setup - Remote) or controlled by input
3) UI signal 1,2.3 and 8 must be ON (IMSTP, HOLD, SFSPD, Enable)
4) MENU/SETUP/PROG Select - RSR/PNS/STYLE... Setup of remote start system
Steps 1-3 makes remote start possible. Step 4 defines method which will be used for remote start:
RSR (Robot service request) - one signal is dedicated for each of RSR inputs and starts specified RSR program
PNS (Program number select) - set of binary inputs (PNS1-PNS8) is translated to decimal number and PNS with corresponding decimal number is started
Style - each Style signal has predefined name of program which will be started
Other - one program specified in variable $shell_wrk.$cust_name is started when UI[6] is On
Depending on program select and program start option you must use appropriate UI signals. (RSR, PNS+PNSTROBE+PRODSTART and so on)
Tomas
So there is no option to use only UI5 and UI6? I must jump those 1,2,3 and 8 inputs, so they would be always ON ?
I think so, but you can make them always ON internally by association with Rack 35 Slot 1 Start 1, so you don't have to use DIs.
Tomas
UI1, UI2, UI3 must be jumped. Other that that you can use only the the one you need
It works great with association with Rack 35. Tomas, thanks a lot for such detailed help