Hi everyone. I hope that someone can give me a pointer on this error and hints on how to correct.
I am commissioning a used Kuka robot into a new installation. The system is a KRC2 controller running WPe and KSS 5.2.12. The robot controller has a multi power tap A30 module. The devicenet output from the mfc card is connected to the MPT and from there 2 devicenet nodes are connected - one to a PLC (node 30) and one to a Renishaw RMP60 measuring unit (node 5)
On power up of the controller, we go to the windows desktop, which has KRC on it. Then upon starting KRC, it starts up and goes into the normal screen however we get an extensive list of errors, the first of which is "error #6502 Error during reading INI file init/iosys.ini 1" There are multiple other "error 6502", referring to ; init/motiondrv.ini 1 ; HW_INF.INI ; PROGRESS.INI ; and MEMCONFIG.INI
There are other errors listed but I think these first items are creating the subsequent faults.
Checking the iosys.ini file it appears OK and the correct devicenet driver is installed and enabled.
First question - does anyone have the documentation on configuring the A30 Multi Power Tap?? I cannot see in the iosys.ini file how the devicenet nodes on the multipower tap are configured and enabled - there are no active DNSCx drivers - does the Multipower tap need this defined?
Symptoms that exist along with the error listing are: devicenet is not working as the PLC on node 30 is not seeing any of the KRC outputs (eg robot in T1 mode even though this bit is set). Also the RJ-45 X804 connection on the mfc appears not be working, and if I connect a ethernet switch to the RJ-45 X804 socket I get a "RTWLoadVxD(LPVXWRT).(#0x1) device driver could not be initated (not found or wrong path). In a number of ways this is similar to the thread started by Martin H in Aug 2007 on the robot-forum.de site, with very similar hardware - though he didn't make mention to the error 6502. The original Kuka wiring diagram for the controller refers to the X804 as either a DSEIBS3AUX or DSEIBSC33. The system also had an X33 plug added to the robot at some time in the past - which today I discovered has been disconnected - I suspect when the unit was upgrade to run XP and the radio measuring probe added (but this is supposition).
Any and all suggestions are greatfully received.