how do I go About fixing this error. it says "DC-Link Incoming Mains not Valid,Drive System 1". "check Voltage from Motor On contactor. Replace DC-Link.". Dc-Link has been Replaced, Voltage from contactor is 262. What can I look into next. Robot has been down a week and we are unable to fix this problem.
39103 Drive System Error
-
LuiCastor -
July 22, 2013 at 10:36 PM -
Thread is Resolved
-
-
We had this tonight when we came in. Replaced K2 and Aux adder block. So far so good.
Theory is that contacts on adder block were bouncing. -
Thanks for your reply Red0492. I will try that next.
-
Salve, a me è successo lo stesso problema, nessun tecnico riesce a risolvere.
Potete dirmi esattamente cosa sono i blocchi K2 e il blocco aux, grazie
-
What series controller do you have, S4C, S4C+ or IRC5?
Which controller model, M97 .... M2004?K2 in the example would be the 2nd Motor On contactor along with its attached auxiliary contact block.
-
Salve, ho un s4 controller, m98 del 1999. Ho cambiato le.bobbine k2 e k1, ma devo aver invertito qualche cavo nel k2, ora mi dà errore 37001.
-
Added manual at IRB6400 M98 manual
This has the controller prints with K1 & K2 connections and wire #s on PDF page 419 (sheet 16 of 54)
-
Grazie mille, chiamo un elettricista e faccio controllare . Gentilissimo
-
Eccomi nuovamente qui... Purtroppo il problema non sono le bobine, a vuoto la tensione è 24, come collego le bobine la.tensione si abbassa a 8v. Non riusciamo a capire qual è l alimentatore.grazie a chi mi aiuta...
-
With meter lead (1) connected to the controller frame, what voltages are at contactors K1 & K2 coils?
Contactors off
K1-A1 =
K1-A2 =
K2-A1 =
K2-A2 =Contactors on
K1-A1 =
K1-A2 =
K2-A1 =
K2-A2 =