Good morning all.
I searched the forums and found a couple of times this was talked about but none of them explained the same issue.
I have 3 R30iBs connected to an AB Compact Logix and Red Lion HMI with a SICK safety controller. When I connect the workcell to our plant network I get a "PRIO-096 SNPX Connection is full" error. See attached screenshot. If I disconnect this from our network then the error never occurs. Any ideas as to what could be causing this?

Thanks

Today at 09:10:41 AM
Reply #1

Advertisement

Guest

February 14, 2019, 10:55:54 PM
Reply #1
Offline

tacheson


PRIO-096SNPXConnectionisfull<%s>
Cause:Numberofconnectionhasreachedsetvalue
Remedy:Doanyoneofthefollowings:Waitaconnectionbecomesvacant,Changesetvalue,Cyclepowerandbeginthebeginningconnection

I'm not sure if this helps or not, but this is the cause and remedy of that alarm.  I'd chat with your IT department and see if they have limits or static limits setup.



Share via facebook Share via linkedin Share via pinterest Share via reddit Share via twitter

question
R30iB PRIO-096 SNPX ERROR

Started by jleblanc on Fanuc Robot Forum

6 Replies
1751 Views
Last post February 25, 2018, 05:20:03 PM
by jleblanc
xx
PRIO-063 Bad I/O asg error. How to fix?

Started by ap2016 on Fanuc Robot Forum

9 Replies
5256 Views
Last post July 04, 2017, 12:57:45 PM
by ap2016
xx
PRIO-600 Profinet Error

Started by Nation on Fanuc Robot Forum

3 Replies
2038 Views
Last post July 07, 2015, 01:34:39 PM
by Nation
question
PRIO-230 Ethernet/Ip Error

Started by hugogalarza on Fanuc Robot Forum

5 Replies
7907 Views
Last post November 14, 2014, 12:12:08 AM
by DuhbCakes