June 05, 2019, 02:42:38 PM
Read 396 times
Offline

pramtekkar


I am new at socket messaging and got this code for communication between cognex and fanuc. I made few modification.
I have few doubts.

Question
1) What will the code line mp_str=''  will do ?
2) the status of the connection is coming a hug number not a 1 or a 0 ? How should I approach?
3) What does   READ file_var (xs::0::2, ys::0::2, angles::0::2) represent?
4)  READ file_var(mp_str) ?? the file_var will access which file or variable from the cognex? Where am I able to get all the variables read in the fanuc tp pendant?


PROGRAM SOCKET_MESSAGING
%COMMENT = 'KL_MAIN V9.1'
%STACKSIZE = 8096
%NOLOCKGROUP
%NOPAUSESHFT
%NOPAUSE = ERROR + COMMAND + TPENABLE
%NOBUSYLAMP
%NOABORT = ERROR + COMMAND
%INCLUDE KLEVCCDF                   -- predefined key character code constants
%INCLUDE KLIOTYPS                   -- karel IO type definitions
%INCLUDE KLEVKEYS                   -- predefined karel key code constants
%INCLUDE KLEVKMSK                   -- predefined mask codes for built in functions

VAR
 file_var  : FILE                     -- for client communication
 tmp_int  : INTEGER
mp_str   : STRING[128]
 status    : INTEGER           -- communication status
entry       : INTEGER
 try          : INTEGER
statuss     :STRING[1]
 xs          :STRING[9]
 ys          :STRING[9]
 angles   :STRING[9]
 x            :REAL
 y            :REAL
angle      :REAL


CONST
port_number= 23  --- Socket port number

BEGIN
   
  SET_FILE_ATR(file_var, ATR_IA)
  SET_VAR(entry,'*SYSTEM*','$HOSTC_CFG[3].$SERVER_PORT',port_number,status)

-- Connect the tag
  WRITE TPDISPLAY('Connecting…',CR)
  MSG_DISCO('C3:', status)  -----   closing port before start
 -- Need to be called before any tag can be used for socket messgaing (1st parameter is the tag name ,2nd parameter integer that will contain status of the operation)
  MSG_CONNECT ('C3:',status)
  WRITE('Connect Status =',status,CR)
  OPEN FILE file_var('rw','C3:')
 
  -- Read the In-Sight Welcome message
  WRITE TPDISPLAY('Logging In',CR)
  mp_str =''
  READ file_var(mp_str)
  WRITE TPDISPLAY(mp_str,CR)

  -- Read User: prompt
  READ file_var(mp_str::6::0)
  IF UNINIT(mp_str) THEN
    mp_str = ''
  ENDIF
  WRITE TPDISPLAY(mp_str,CR)
  IF (mp_str <>'User: ') THEN
    WRITE TPDISPLAY('User Failed',CR)
    --Error
    RETURN
  ENDIF

  --Send User Name
  WRITE file_var('admin',CHR(13),CHR(10))

  -- Read Password prompt
  mp_str =''
  READ file_var(mp_str::10::0)
  IF UNINIT(mp_str) THEN
    mp_str = ''
  ENDIF
  WRITE TPDISPLAY(mp_str,CR)
  IF (mp_str <>'Password: ') THEN
    WRITE TPDISPLAY('Password Failed',CR)
    --Error
    RETURN
  ENDIF

  --Send Password
  WRITE file_var('',CHR(13),CHR(10))

  -- Read Login Response
  mp_str =''
  READ file_var(mp_str)
  IF UNINIT(mp_str) THEN
    mp_str = ''
  ENDIF
  WRITE TPDISPLAY(mp_str,CR)
  IF (mp_str <> 'User Logged In') THEN
    WRITE TPDISPLAY('Log In Failed',CR)
    --Error
    RETURN
  ENDIF

  -- Instruction In-Sight to Acquire an Image
  -- (wait for a response)
  WRITE TPDISPLAY('Trigger',CR)
  WRITE file_var ('sw8',CHR(13),CHR(10))
 
  -- Read Status
  READ file_var (statuss)
  IF statuss <> '1' THEN
    WRITE TPDISPLAY('sw8 Failed',CR)
    RETURN
  ENDIF
 
  -- Get the value in cell C7
  WRITE TPDISPLAY('Get Value C7',CR)
  WRITE file_var ('gvc007',CHR(13),CHR(10))
 
  -- Read Status
  READ file_var (statuss)
  IF statuss <> '1' THEN
    WRITE TPDISPLAY('gvc007 Failed',CR)
    RETURN
  ENDIF
 
  -- Read the data
  -- This will split the information at the quotations "'".
  -- Example String '10.5''9.8''15.9'
  READ file_var (xs::0::2, ys::0::2, angles::0::2)

  --Disconnect Socket
  MSG_DISCO('C3:', status)

  -- Convert the data
  CNV_STR_REAL(xs, x)
  CNV_STR_REAL(ys, y)
  CNV_STR_REAL(angles, angle)
  WRITE TPDISPLAY('X:',x,CR,'Y:',y,CR,'R',Angle,CR)

END SOCKET_MESSAGING


Today at 03:36:46 PM
Reply #1

Advertisement

Guest

June 07, 2019, 12:56:39 PM
Reply #1
Offline

MIRobotGuy


Hello,
Although I am not an expert, I will take a stab at answering these questions...

1) What will the code line mp_str=''  will do ?
A) This instruction will clear the string before reading it, so that data from the next line will be the only data in this variable, and there will be no residual data.

2) The status of the connection is coming a hug number not a 1 or a 0 ? How should I approach?
A) I have created an Excel file that will convert the status value to an error code.  Then the error code can be researched in the Fanuc eDocs.  I believe this may help point you in the right direction.
https://www.robot-forum.com/robotforum/tools-for-fanuc-robots-(no-manuals-permitted-by-order-of-fanuc-robotics)/fanuc-karel-status-converter/


3) What does   READ file_var (xs::0::2, ys::0::2, angles::0::2) represent?
A) This will read the string values from the cognex system.  xs, ys, and angles are all strings of 9 characters long.  The numbers ::0 and ::2 are format specifiers.  Look in the KAREL eDocs under 7.8 FORMATTING TEXT (ASCII) INPUT/OUTPUT for more information about these.

4) READ file_var(mp_str) ?? the file_var will access which file or variable from the cognex? Where am I able to get all the variables read in the fanuc tp pendant?
A) similar to #3

I hope this helps,
MiRobotGuy
+-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=+
MI Robot Guy

June 07, 2019, 03:28:00 PM
Reply #2
Offline

Witty


Regarding question 3:
Take a look at the example string provided: '10.5''9.8''15.9'.
Code: [Select]
READ file_var (xs::0::2, ys::0::2, angles::0::2) would cut this example string into substrings to xs, ys, angles with " being the separator. Unfortunately, I can recall, that you can't use " as separator in Cognex - correct my if I'm wrong. So what Cognex might actually send to you will be more like '10.5,9.8,15.9', and you will have to separate the numbers yourself.

Regarding question 4:
"The file_var will access which file or variable from the cognex?"
The ones which you request with Get Value command. In this example code, there's:
Code: [Select]
WRITE file_var ('gvc007',CHR(13),CHR(10))So from Fanuc you're sending a command to Cognex, saying: "Get me value of C7". And as an anwer, cognex will send you this value.
In Cognex In-Sight Explorer you configure the output for the robot system to be available under "Job.Robot.FormatString", so the command to get your inspection results from Cognex would be:
Code: [Select]
WRITE file_var ('gvJob.Robot.FormatString',CHR(13),CHR(10))

June 10, 2019, 02:54:13 PM
Reply #3
Offline

ESIELI


I have done this many times via serial communication. It may differ a little from your code because you're doing socket messaging, but you can see my setup info and code used on my website:
https://bateautomation.com/2019/01/03/cognex-fanuc-setup/


Thank you

July 10, 2019, 10:36:46 PM
Reply #4
Offline

pramtekkar


thank you all for the help. I data format to be transferred from cognex 3d scanner can be in the Ascii type, 16 bit- signed integer and soo on. Please see the attachment. I have created variable in my karel program to accept this data. Ca you please let me know if the variables I declared are wrong and wont accept the data ?
is my line of code to read the file from cognex application correct?

PROGRAM  Cognex
%COMMENT = 'KL_SocketMessaging V9.1'
%STACKSIZE = 8096
%NOLOCKGROUP
%NOPAUSESHFT
%NOPAUSE = ERROR + COMMAND + TPENABLE
%NOBUSYLAMP
%NOABORT = ERROR + COMMAND
%INCLUDE KLEVCCDF                   -- predefined key character code constants
%INCLUDE KLIOTYPS                   -- karel IO type definitions
%INCLUDE KLEVKEYS                   -- predefined karel key code constants




VAR      ---- Global Variable declaration
 file_var  : FILE              -- for client communication
 enc_count: INTEGER
tmp_int  : INTEGER
tmp_int1  : INTEGER
tmp_str   : STRING[128]
status    :  INTEGER           -- communication status
entry       : INTEGER
 try          : INTEGER
 xs          : STRING[128]
 ys          : STRING[128]
 angles   : STRING[128]
 x            : REAL
 y            : REAL
angle      : REAL
comment : STRING[16]
loop1 :BOOLEAN
my_pos :XYZWPR



BEGIN
   
 MSG_PING('S3:',status)
 WRITE TPDISPLAY('pinging',status)
   
  SET_FILE_ATR(file_var, ATR_IA)
  SET_VAR(entry,'*SYSTEM*','$HOSTC_CFG[3].$SERVER_PORT',5001,status)

-- Connect the tag
  WRITE TPDISPLAY('Connecting…',CR)
  MSG_DISCO('S3:', status)  -----   closing port before start

  MSG_CONNECT ('S3:',status)
  WRITE('Connect Status =',status,CR)
  loop1= TRUE
 
 IF status = 0 THEN
      WHILE loop1 = TRUE DO
              WRITE TPDISPLAY('OPENING FILE..',CR)
               OPEN FILE file_var('RW','S3:')
               status=IO_STATUS(file_var)
                                IF status = 0 THEN
                                          FOR tmp_int =1 TO 10 DO
                                           READ file_var(tmp_str ::10)
                                           READ file_var(tmp_int ::10)
                                                          IF status <> 0 THEN
                                                                               WRITE('Loop Test Fails',CR)
                                                                                loop1 = FALSE
                                                                                tmp_int = 10
                                                           ENDIF
                                        ENDFOR
                                  ENDIF
           ENDWHILE
 ENDIF
 
 READ file_var(xs::10)
 READ file_var(ys::10)
 READ file_var(ys::10)
WRITE TPDISPLAY ('disconnecting', CR)
       MSG_DISCO('S3:',status)  --Disconnect Socket
 
  -- Convert the data
  CNV_STR_REAL(xs, x)
  CNV_STR_REAL(ys, y)
  CNV_STR_REAL(angles, angle)
 WRITE TPDISPLAY('X:',x,CR,'Y:',y,CR,'R',Angle,CR)
END Cognex

Please let me know how can I proceed to get the right data in the correct format.
How can I read daa from the cognex file into group inputs?


Share via facebook Share via linkedin Share via pinterest Share via reddit Share via twitter

moved
MOVED: Communication going between cognex and fanuc robot

Started by SkyeFire on General Discussion of Industrial Robots Only

0 Replies
124 Views
Last post June 05, 2019, 03:13:03 PM
by SkyeFire
xx
Fanuc / Cognex EIP communication

Started by worseltes on Fanuc Robot Forum

5 Replies
6278 Views
Last post December 16, 2015, 09:39:40 PM
by ESIELI
xx
communication with an intelligent camera (cognex)

Started by Karisma on Fanuc Robot Forum

8 Replies
5437 Views
Last post January 11, 2016, 06:25:02 PM
by ESIELI
question
KUKA communication with Cognex In sight

Started by Robin de Bree on KUKA Robot Forum

16 Replies
2164 Views
Last post June 12, 2018, 12:21:38 PM
by panic mode