Had a split pendant cable. Replaced now get this error. Checked cable....fuses...etc. Any other suggestions

Today at 08:59:32 AM
Reply #1

Advertisement

Guest

December 20, 2018, 12:52:44 PM
Reply #1
Offline

Lemster68


Sounds like S4C+ or earlier, right?  Reboot yet?

December 29, 2018, 09:36:43 AM
Reply #2
Offline

hydra


Do you have another Teach Pendant you can try? If there is no error in the system when Teach Pendant is not connected. The controller needs to be opened. The Motor On lamp should flash. If the teach pendant stays on this screen; When the teach pendant is plugged in, disconnect and re-energize the system. Still this screen is not going; reinstall the system. System; S4C or S4C +?
Think before you talk, Read it before you think about it.
-Fran Lebowitz.

-----------------------------------------------------

info@hbarobot.com
http://www.hbaotomasyon.com/en/index-en.aspx

March 11, 2019, 07:45:37 PM
Reply #3
Offline

Замира Зуваитова


hmm, hello everyone!!! i have the same problem today S4 irb6400 m98, Teach pendant communication lost(. "motor lamp on" is not on flashing. EN led indicator also not on, blinking couple of time when turning on the controller and then different errors.. In Friday it was working pretty good, on Monday showing an error. Might it be because of the power supply outlet +5 or +-15W? ( i am thinking because of Motor Lamp On" is not flashing). Booting time is taking about 20 minutes till it shows different error
« Last Edit: March 11, 2019, 07:48:47 PM by Замира Зуваитова »

March 13, 2019, 01:17:38 AM
Reply #4
Offline

Skooter


Just to be clear, the robot boots up to where the network status (NS) LED on the panel board is green but the teach pendant display still says "Teach pendant communications lost".  Is that correct?

Does this mean the teach pendant now shows other errors on the display after 20 minutes?  If so, what are those errors?

March 13, 2019, 08:40:27 AM
Reply #5
Offline

Замира Зуваитова


[quote author=Skooter link=topic=30105.msg130229#msg130229 date=1552439858]
Just to be clear, the robot boots up to where the network status (NS) LED on the panel board is green but the teach pendant display still says "Teach pendant communications lost".  Is that correct?

 - Not really. In the beginning it says "Teach pendant communications lost", do not open "welcome ABB" screen, all the LED on panel board is green.
« Last Edit: March 13, 2019, 08:42:31 AM by Замира Зуваитова »

March 13, 2019, 08:51:23 AM
Reply #6
Offline

Замира Зуваитова


the same boot -  In the beginning it says "Teach pendant communications lost", do not open "welcome ABB" screen, all the LED on panel board is green. Booting takes about 20 min, then the errors. Teach pendant do not react at all when i push any button. Even do not move "the cursor" to see the next error.  only beeps. Motor ON lamp does not flash.
« Last Edit: March 13, 2019, 09:46:29 AM by Замира Зуваитова »

Today at 08:59:32 AM
Reply #7

Advertisement

Guest

March 14, 2019, 12:45:17 AM
Reply #7
Offline

Skooter


The 'Welcome ABB' only comes up when the controller boots up without errors.  The S4C & S4C+ take a very long time to boot when there are system errors.
Are there any other errors that happen before the Internal errors?
Focusing on why the teach pendant does not respond to key presses:
Could be the teach pendant is receiving but transmitting - try another teach pendant.
Could be an issue with the Panel Unit - try another.
Unplug the backplane X10 & X16 CAN bus connections and try again.  Perhaps something is loading the CAN bus after a while.
Could be a fatal error in the system that requires a software reload.  The errors are on the screen are not encouraging.  I hope you have a recent backup and software just in case.
You could monitor the output of the serial port on the front of the Main Computer board.  Search the ABB & ABB manuals board for "PC as service tool" for more info.

March 15, 2019, 11:09:32 AM
Reply #8
Offline

Замира Зуваитова


problem is solved by reinstalling the system, everything is working. Thanks for your replies and support.


https://www.youtube.com/watch?v=SwU6f6Xkud8


Share via facebook Share via linkedin Share via pinterest Share via reddit Share via twitter

clip
Teach pendant communication lost

Started by zdravо on ABB Robot Forum

2 Replies
2263 Views
Last post May 31, 2017, 03:11:02 AM
by Skooter
xx
Teach pendant communication lost s4c m98 (first time during running a program)

Started by Kroket on ABB Robot Forum

1 Replies
2523 Views
Last post March 16, 2014, 01:36:51 PM
by Kroket
xx
Problem Teach pendant communication lost at the time of installation of the RW.3

Started by kennedyrsb on ABB Robot Forum

1 Replies
378 Views
Last post August 14, 2018, 01:46:04 PM
by kennedyrsb
xx
No communication to teach Pendant

Started by alexspears77 on Fanuc Robot Forum

1 Replies
294 Views
Last post August 15, 2018, 09:52:56 AM
by stare284