Has anybody had any success with setting up Safemove2 and using CIP Safety to talk to an Allen Bradley safety PLC? We are trying to do this for the first time and are having no luck. When trying to establish the connection the PLC is giving us an error, "Connection Request Error: Invalid segment type"

Linkback: https://www.robot-forum.com/robotforum/index.php?topic=26545.0

Today at 06:18:45 AM
Reply #1

Advertisement

Guest

April 20, 2018, 01:42:00 PM
Reply #1
Offline

roulv


Probably your assembly instance are wrong in PLC.
Check if Safety Input connection has:
  -Input assembly instance equal configured on SafeMove.
  -Input size equal configured on SafeMove.
  -Output assembly instance must be null (199)
  -Configuration assembly instance must be null (199)

Check if Safety Output connection has:
  -Output assembly instance equal configured on SafeMove.
  -Output size equal configured on SafeMove.
  -Input assembly instance must be null (199)

Check if Standard connection has:
  -Input assembly instance equal configured on SafeMove.
  -Input size equal configured on SafeMove.
  -Output assembly instance equal configured on SafeMove.
  -Output size equal configured on SafeMove.
  -Configuration assembly instance must be null (199)
  -Configuration size must be 0

April 20, 2018, 03:30:51 PM
Reply #2
Offline

bellm


Thank you for the reply, after changing the configuration size to 0 I know get a message "Connection Request Error: Module connection limit exceeded." Have any suggestions? I tried resetting the CIP connection in the teach pendant.

April 26, 2018, 01:40:48 AM
Reply #3
Offline

jstolaruk


What A-B hardware are you using, specifically part numbers of the PLC and if 1756 series the ethernet module.

April 26, 2018, 01:31:25 PM
Reply #4
Offline

bellm


We are using a L30ERMS. What I believe the issue was, was that our EtherNet I/P device in the robot was set to 8 bits in/out. I changed this to 16 and set the RPI to 20000 instead of 30000 and I was able to get it working.

Today at 06:18:45 AM
Reply #5

Advertisement

Guest

May 01, 2018, 03:41:27 PM
Reply #5
Offline

penguinMan


I am having the same issue, however in Safemove where it says NodeID - if i change this address i get a fault saying the ip address has to match the industrial network which is by default 192.168.125.1 .. our network is running 192.168.1.XXX. How do i change it so the PLC reads the safemove IO in CIP

May 01, 2018, 03:49:23 PM
Reply #6
Offline

bellm


I was given a cheat sheet from ABB to assist in getting started, I have linked it here.


Share via facebook Share via linkedin Share via pinterest Share via reddit Share via twitter

xx
SafeMove2 GSD file error

Started by londoneye on ABB Robot Forum

2 Replies
1527 Views
Last post October 24, 2016, 06:18:58 PM
by jstolaruk
xx
ABB IRC5 CHANGE SAFETY USER PASSWORD FOR SAFETY SYNC

Started by Biomed500 on ABB Robot Forum

1 Replies
2193 Views
Last post December 03, 2016, 11:48:28 AM
by fluke
xx
MRC, safety door connect ot External Safety Inputs????

Started by raska_rob on Yaskawa Motoman Robot Forum

3 Replies
2237 Views
Last post October 21, 2014, 08:39:07 PM
by Pcarbines
xx
Safety output on XRC -> to external Safety relay

Started by cisco_x on Yaskawa Motoman Robot Forum

3 Replies
1545 Views
Last post October 21, 2014, 06:33:55 PM
by Pcarbines